#113292 - 04/08/02 09:28 PM No Main Breaker?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA


Was this panelboard legal for use as Service Equipment? If so, were there any restrictions? There was no label inside the cover.

Bill
Top
Tools for Electricians:
#113293 - 04/09/02 03:08 AM Re: No Main Breaker?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
with a 4th wire....maybe
Top
#113294 - 04/09/02 05:18 AM Re: No Main Breaker?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Sparky,

If you look at the lower Buss there are 12 spaces there. This panel could easily (and did) exceed the maximum # of disconnects. The only way it could comply would be with all 2 pole breakers installed there and that's not likely to happen.

Bill
Top
#113295 - 04/09/02 06:06 AM Re: No Main Breaker?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
This "split-bus" panel typically has 6 double-pole breakers as the "power section" feeding the range, dryer, AC, etc. Also, a 50 or 60 amp breaker to feed the "lighting" section in the top half. Used in this manner, it would meet the "six operations of the hand" rule with regard to Servive Disconnect.
However, if it is considered a lighting & appliance panel (which it probablty is) it would require a main.
Correct?
Top
#113296 - 04/09/02 06:36 AM Re: No Main Breaker?
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I still don't understand the advantages of a split bus...

Assuming the bus is protected at 200A, the "sub" breaker feeding the smaller bus is redundant, takes up space, and seems just plain silly...

If there is an advantage, can we have this advantage in the extreme? Let's have a split bus and a sub-feed breaker for every circuit!

(See my point?)
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#113297 - 04/09/02 08:26 AM Re: No Main Breaker?
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
Bill,

This was suitable for use as Service Equipment. From your photo, the lower 12 pole section was for the "Mains" (before we started calling them Service Disconnects). Then, as now, there could only be a maximum total of six operations of the hand to disconnect the service from the load (up to 6 single poles breakers, 6 double pole or a mixture totalling to a max of 6). The size of the service conductors were based on the calculated load at the time of installation, plus any room for expansion that may, or may not, have been added.

I look at this photo and see it as upside down. I helped install a lot of residential split-bus panels when I was apprenticing.

Even with the "Lighting Section" bus being rated for tandem breakers, over time, I've seen these fill up, and the "open spaces" in the "Main Section" mistakenly (or deliberately) used for branch circuits.

As always, there's no accounting for those who will do anything to get the job done quick and cheaply.

Al
_________________________
Al Hildenbrand
Top
#113298 - 04/09/02 08:41 AM Re: No Main Breaker?
ElectricAL Offline
Member
Registered: 10/10/01
Posts: 597
Loc: Minneapolis, MN USA
'66

The real attraction to this was the lower material cost. I remember a lot of GE panels, bus only, not a single breaker in them. The leads to the "Lighting Section" were factory installed, but the choice of breaker was up to the installing electrician. If all the "Mains" are 70 Amp or smaller, the higher cost breakers are not used.

Al
_________________________
Al Hildenbrand
Top
#113299 - 04/09/02 12:19 PM Re: No Main Breaker?
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Al,

I see it as upside-down too. I see quite a few panelboards (even with main) installed upside-down presumably to save a few feet of cable. I don't remember seeing ones like this with so many spaces (12). Can you tell if this neutral bar is bonded? I don't see a strap.

I don't thonk this was the original panelboard for this house, It was most likely a 100A originally because there was a #6 solid Al cut just above the panel and a #4 Al running to the water main.

Bill
Top
#113300 - 04/09/02 01:01 PM Re: No Main Breaker?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
spark,

The bus isn't protected at 200 amp. It is not protected at all. These panels are fed directly from the meter. They were not sub-panels. I guess the cost advantage was in not supplying a 200 amp main breaker.
Top
#113301 - 04/09/02 04:38 PM Re: No Main Breaker?
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I mistook it for a mis-wired sub......
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 67 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals