#113159 - 03/13/02 02:48 PM Pool Timer
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA

Quote:
The timeclock is feed with 6/2 WG connected to a 60 A 2 pole. It supplies three motors 1-2HP 1-11/2HP 1- 1/2HP for the swimming pool. Each motor is connected with 12/2 WG-NMB. Pool man's tap rules I guess.The location of the timer is in the 1000SQFT plus pool house. The property is conservatively 600 thousand dollars. The pool light had never been connected but was wired with no GFCI or bonding. Picture of CT cabinet on the pool deck is a coming attraction if it doesn't make the coroners photos before mine.

WATTHEAD
Top
Tools for Electricians:
#113160 - 03/13/02 04:22 PM Re: Pool Timer
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
It looks like a weatherproof timer is in order! Good thing you caught this before something bad happened!
_________________________
Peter
Top
#113161 - 03/13/02 07:12 PM Re: Pool Timer
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
Sorry about the spelling it should have been feeded with a 6/2WG It is feed fed feeded isn't it?
Top
#113162 - 03/14/02 06:57 PM Re: Pool Timer
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
You must be kidding!!
This timer shouldn't be connected to a 60A circuit.
Wake up and address some of the problems here!!
Top
#113163 - 03/15/02 03:48 PM Re: Pool Timer
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
The picture is only to show what you run into on a daily basis in an area that has inspectors on the payroll and regularly takes permit money from me. The timer and associated wiring were junked, and a panel was mounted with individual 20 amp breakers for each motor. I will try to post a picture so you guys can gig me on the installation.
watthead
Top
#113164 - 03/15/02 06:15 PM Re: Pool Timer
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Watthead,

Looking at this picture I can almost taste the pool chemicals.

Yuucckkk!

Bill
Top
#113165 - 03/19/02 06:42 PM Re: Pool Timer
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Honest, if you post a "better than" pic, I'll be a happy guy.
There are so many violations here that I was left nearly speechless. An uncommon thing for a big mouth like me
Top
#113166 - 03/22/02 03:59 PM Re: Pool Timer
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA

Quote:
Ripped out pool timer and replaced with a panel, a new timer, and some X-10 switches so the owner can turn on the jets to the spa without having to touch the switch after he has been in the pool or spa. (remote control transmitter only has a 3.2v battery) I have nightmares about a soaked swimmer operating a non-gfci switch.


Quote:
Recessed panel and timer because Bill was right on the money about the pool chemicals that were eating up the previous timer switches etc. PVC conduit run around wall with carflex drops to motors. O.K. gentelmen fire at will.

watthead
Top
#113167 - 03/22/02 05:14 PM Re: Pool Timer
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
hmm, mighty clever with the X-10's there...
Top
#113168 - 03/23/02 05:38 AM Re: Pool Timer
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Very Nice!!
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 91 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals