#113022 - 01/30/02 03:58 PM Remodel Box
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA

Quote:
This remodel box is a plastic type, cut into a kitchen cabinet, fed with a #14-3 NM-B cable which enters directly to the left of the box, as seen between the cabinet and wall. Notice 2nd open ko behind ko which has cable in it. No clamp is used.


Electrician (20 years +) is trying to use Section 370-17 (c) exception (1999 NEC) for code compliance. Any comments?


Rick Miell
Top
Tools for Electricians:
#113023 - 01/30/02 04:29 PM Re: Remodel Box
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The exception applies to boxes mounted in a wall or ceiling. This isn't either. It's a cabinet.
Top
#113024 - 01/31/02 03:54 AM Re: Remodel Box
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
I always thought this exception addressed plastic nail-on boxes which need to be stapled within 8 ".
BTW, does punching a hole in the side of an old-work box violate 110-2(b)? (99 NEC)
Top
#113025 - 02/10/02 03:23 PM Re: Remodel Box
Elzappr Offline
Member
Registered: 12/20/01
Posts: 270
Loc: Oregon
Just to clear things up, the exception to 370-17(c) still requires that NM cable enters the box through a "cable knockout". From what I can see in the photo, the cable is entering through a conduit knockout.
Redsy's comment was correct..that the exception is more pertinent to the notion that you can staple the unclamped wire within 8", measured along the wire, and an exception to the usual 12" allowed in Article 336.
Top
#113026 - 03/14/02 01:06 AM Re: Remodel Box
seymo1 Offline
Junior Member
Registered: 03/14/02
Posts: 4
Loc: Dallas, TX USA
i don't think that is a knockout at all...just a hole drilled in the side. you can see where they failed on the first attemt.
Top
#113027 - 03/14/02 07:21 PM Re: Remodel Box
spkjpr Offline
Member
Registered: 12/01/00
Posts: 218
Loc: Sedalia,MO, USA
I don't recall ever seeing any of the plastic boxes that had a conduit KO or hole in the side of the box. Could this be a possible listing violation?
Top
#113028 - 03/15/02 03:54 PM Re: Remodel Box
watthead Offline
Member
Registered: 10/13/01
Posts: 172
Loc: South Carolina
what seymo said
watthead
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals