#112968 - 12/30/01 03:29 PM Is this Code compliant?
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA


Is this installation Code compliant?

- Electure

Top
Tools for Electricians:
#112969 - 12/30/01 03:57 PM Re: Is this Code compliant?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
In addition to lack of proper workspace in front of the disconnect covered by Article 110 the following rule is also violated.

Was this another one that fell through the $$$ cracks?

440-14. Location
Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
_________________________
Joe Tedesco, NEC Consultant

Top
#112970 - 12/30/01 04:03 PM Re: Is this Code compliant?
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
I believe you would also find that ALL the mounting holes must be covered to keep the 3R rating of the disconnect.

Top
#112971 - 12/30/01 05:03 PM Re: Is this Code compliant?
Nick Offline
Member

Registered: 08/13/01
Posts: 603
Loc: Riverside, CA
Will the cover even open?!

Top
#112972 - 12/31/01 10:23 AM Re: Is this Code compliant?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The cover will open all the way.

So, does this qualify as a piece of equipment that will be "likely to require examination, adjustment, servicing, or maintenance while energized" per 110.26(A)?
You've got to shut it off to open the cover.

(George wins the prize, it already has some evidence of water damage inside. One good El Nino winter and it's history)

Top
#112973 - 12/31/01 03:21 PM Re: Is this Code compliant?
Redsy Offline
Member

Registered: 03/28/01
Posts: 2138
Loc: Bucks County PA
electure,

I would say 110.26(A) applies. You might need to check incoming voltage.

Top