#112968 - 12/30/01 03:29 PM Is this Code compliant?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA


Is this installation Code compliant?

- Electure
Top
Tools for Electricians:
#112969 - 12/30/01 03:57 PM Re: Is this Code compliant?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
In addition to lack of proper workspace in front of the disconnect covered by Article 110 the following rule is also violated.

Was this another one that fell through the $$$ cracks?

440-14. Location
Disconnecting means shall be located within sight from and readily accessible from the air-conditioning or refrigerating equipment. The disconnecting means shall be permitted to be installed on or within the air-conditioning or refrigerating equipment.
_________________________
Joe Tedesco, NEC Consultant
Top
#112970 - 12/30/01 04:03 PM Re: Is this Code compliant?
George Corron Offline
Member
Registered: 05/16/01
Posts: 717
Loc: Lorton, Va USA
I believe you would also find that ALL the mounting holes must be covered to keep the 3R rating of the disconnect.
Top
#112971 - 12/30/01 05:03 PM Re: Is this Code compliant?
Nick Offline
Member
Registered: 08/13/01
Posts: 599
Loc: Riverside, CA
Will the cover even open?!
Top
#112972 - 12/31/01 10:23 AM Re: Is this Code compliant?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The cover will open all the way.

So, does this qualify as a piece of equipment that will be "likely to require examination, adjustment, servicing, or maintenance while energized" per 110.26(A)?
You've got to shut it off to open the cover.

(George wins the prize, it already has some evidence of water damage inside. One good El Nino winter and it's history)
Top
#112973 - 12/31/01 03:21 PM Re: Is this Code compliant?
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
electure,

I would say 110.26(A) applies. You might need to check incoming voltage.
Top

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 49 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals