#112941 - 12/28/01 09:00 PM Closet Light
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA


What are your thoughts on these fixtures and the way that this one is installed? (this is a clothes closet)

Bill
Top
Tools for Electricians:
#112942 - 12/29/01 02:42 AM Re: Closet Light
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
call the bomb squad...
Top
#112943 - 12/29/01 05:03 AM Re: Closet Light
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Bill:

Violates 410-8 because "lampholders" are not allowed in a clothes closet. This is not a "fixture", common error by many calling it one.
_________________________
Joe Tedesco, NEC Consultant
Top
#112944 - 12/29/01 05:33 AM Re: Closet Light
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Joe,

Thanks for the correction, I should have put the word in 'quotes' as I was not sure what to call it. Were these ever legal for use in clothes closets? I'm also wondering about the situation with the cord being stapled and passing through the doorway. I would think that for these 'Lampholders' to be used a receptacle would have to be on the inside of a closet, which I'll bet was not the standard mode of installation.

Bill
Top
#112945 - 12/29/01 05:53 AM Re: Closet Light
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Bill: Only "fixture" of special types identified in 410-8 are allowed in "clothes closets", I'll bet if we knew who made the product you show here, that the instructions say not to use it in a clothes closes, although I may be wrong --- but who knows -- and we still can buy non dead front cord caps with discs!
_________________________
Joe Tedesco, NEC Consultant
Top
#112946 - 12/30/01 06:32 AM Re: Closet Light
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
They missed a couple of spots when they painted the extension cord.
Any idea where that other plugged in cord goes?
Top
#112947 - 12/30/01 08:22 AM Re: Closet Light
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
electure,

Yes, I do know about the other cord. It goes to a second doorway to the right that leads to the Garage. Yeah, you have to go through a small coat closet to get to the Garage! Kinda neat having secret doors like that. I don't like these lights in there though, or the cord stapled and passing through the doorway.

The house itself is hidden from the street by the landscaping and I couldn't even get in their driveway more than 10 feet because it is made up of several sharp turns designed specifically to disguise itself. I passed it 3 times without seeing it the first time I went there. Someone spent a lot of time and expense laying out the property.

Bill
Top
#112948 - 12/30/01 10:27 AM Re: Closet Light
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
I've often seen similar techniques for closet wiring in this country.

Pardon my ignorance, but what exactly is a non-dead front cord cap? I've often seen references to dead-front plugs etc. but never quite been able to figure out what it refers to.
Top
#112949 - 12/30/01 12:41 PM Re: Closet Light
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Here is what I meant about non-dead front:

_________________________
Joe Tedesco, NEC Consultant
Top
#112950 - 12/30/01 12:53 PM Re: Closet Light
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Paul,

To add a little to Joes'icture there the plastic 'shield' (?) comes off and there are exposed screw terminals below with the stranded wires wrapped around them.

Joe,

Are door-jamb switches considered as being outside the closet?

Bill
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals