#112621 - 07/30/01 07:45 PM Dining Hall Feeder
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA



 Quote:
2000V #6-3 SOW Cable feeding a 200A panel for a dining hall. This hall will be used for the upcoming music festival. I removed the panel cover so I could check voltage drop and amperage concerns after seeing this feed.

With the fryer, lights and oven and cooler running, the current reads about 88 amps per leg... The voltage? 108V and 109V ... That doesn't include coffee pots, beer coolers, heat lamps, etc. etc.

I'm told the feed is fed from a 70A Breaker. (?) It comes from across the road (through rigid pipe not buried) from a dwelling about 250' away, but there is 500' of cable looped back and forth... (the owner didn't want to cut the cable...)

I asked a maintenance man about the dining hall and "no one has had any trouble..." He also said "It's mining wire, it'll handle that building..."

If you look closely, the White Conductor (Hot) and Red Conductor (Neutral) have a small green companion... it appears to be steel cable with a non-dielectric green covering. (Like clothes line wire!)

I will be typing up a disclaimer to cover myself here...

-Virgil



[This message has been edited by Webmaster (edited 07-30-2001).]

Top
Tools for Electricians:
#112622 - 07/31/01 03:40 PM Re: Dining Hall Feeder
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
Virgil,

That is definitely mine cable. The "greens", I believe, are for the ground check circuit.

looks state of the art to me!

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#112623 - 07/31/01 03:45 PM Re: Dining Hall Feeder
Anonymous
Unregistered


>the White Conductor (Hot) and Red Conductor (Neutral)
I'm not coming to help you after all.

Top
#112624 - 07/31/01 08:38 PM Re: Dining Hall Feeder
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I had assumed the greens were "messenger" wire, for strength, marked green to hopefully insure bonding.(?)

They appeared to be steel inside a translucent green sheath, not unlike clothes-line...

Dspark... You ain't seen nuthin' yet!

I see this stuff almost every day... no exaggeration! I'll keep posting the good ones like this... Once again, a macro lens type camera would be more useful for most that I run into... (Due to lack of working clearances and the minimum 3' focus on my current camera, well, you get the idea!)


[This message has been edited by sparky66wv (edited 07-31-2001).]
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#112625 - 08/01/01 04:46 AM Re: Dining Hall Feeder
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
What is is that gives this cable a 2000V rating? The part in the pic doesn't appear to be any different than 600v (or 300V, for that matter) I've never seen mining cable.
Is the 70A C/B an FPE?
This is scary.

Top
#112626 - 08/01/01 05:45 AM Re: Dining Hall Feeder
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
SOW 2000V written right on the jacket...

Mining Cable = SOW
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

Top
#112627 - 08/01/01 12:29 PM Re: Dining Hall Feeder
nesparky Offline
Member

Registered: 06/21/01
Posts: 650
Loc: omaha,ne
thank god we don't see mining cable here
does AHJ or OSHA do any thing there?
_________________________
ed

Top
#112628 - 08/01/01 02:45 PM Re: Dining Hall Feeder
Tom Offline
Member

Registered: 01/01/01
Posts: 1069
Loc: Shinnston, WV USA
NESPARKY,

To paraphrase a famous movie "AHJ? We don't need no stinking AHJ."

Once you get away from a few of the larger cities in the Mountain State, there is no AHJ and pretty much no inspection, except for the service and only if served by one particular power company.

OSHA? They're too busy rousting people with money to pay their fines.

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.

Top
#112629 - 08/01/01 04:47 PM Re: Dining Hall Feeder
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
They really don't need a stinkin' AHJ.
. check out NEC 90-2(b)(2) !!
I don't think they're subject to OSHA either(could be wrong on that).
They're their own AHJ

Top
#112630 - 08/01/01 09:42 PM Re: Dining Hall Feeder
sparky66wv Offline
Member

Registered: 11/17/00
Posts: 2339
Loc: West Virginia
I failed to mention that the odd flair on the end of the entrance conduit is actually the remnants of an LB... The other half was lying on the ground below...

I like the fact that the Fryer/Grille and Range feeders are the same size as the mains!!!

No one (but me) has warned the festival promoters of the lack of ampacity, especially considering voltage drop....

It has apparently already burned up the cooler compressor motor... (browning out)...

And there is no damage waiver to any equipment used during the festival... It's a trap!