ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#112508 - 06/29/01 09:34 PM Air Vents in Wireway
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA

Quote:
Picture is of a 6" x 6" wireway with two PVC air vents running through the middle. The top of the vent is required to be a specific height above the equipment below, so holes were drilled in the wireway and the pipe run through it.

Tom Baker
Top
Tools for Electricians:
#112509 - 06/30/01 04:40 AM Re: Air Vents in Wireway
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
Looks like this violates Section 300-8. Installation of Conductors with Other Systems
Raceways or cable trays containing electric conductors shall not contain any pipe, tube, or equal for steam, water, air, gas, drainage, or any service other than electrical.
_________________________
Joe Tedesco, NEC Consultant
Top
#112510 - 06/30/01 06:12 AM Re: Air Vents in Wireway
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
I guess too, in practicality there may be an issue with sharp edges from the holes that were cut being exposed (if not somehow bushed)

Bill
Top
#112511 - 06/30/01 08:01 AM Re: Air Vents in Wireway
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
it always amazes me that other trades have the unabashed gumption to mess with ours.
Top
#112512 - 06/30/01 12:18 PM Re: Air Vents in Wireway
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
wonder what the other trades would do if you cut out the pvc pipes and plugged the wireway. how did this get by the AHJ?
_________________________
ed
Top
#112513 - 06/30/01 12:52 PM Re: Air Vents in Wireway
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
I had this idea to make rubber mats, 30" x 36", 42" or 48" depending on conditions. These mats would be placed on the floor of areas dedicated to electrical working spaces and would say something in bright yellow letters such as:

"DANGER! ELECTRICAL ZONE... NOTHING GOES HERE as per 1999 NEC 110-16(a). Failure to comply will result in extremely expensive change-order costs and procedures."

Whaddya think?
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#112514 - 07/01/01 09:29 AM Re: Air Vents in Wireway
nesparky Offline
Member
Registered: 06/21/01
Posts: 642
Loc: omaha,ne
like that idea are you sure the general can read?
_________________________
ed
Top
#112515 - 07/01/01 11:04 AM Re: Air Vents in Wireway
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
well Virgil,the idea has merit!

on one job i worked there were some ornery drywallers , you know, the ones with the 4" router bits.....
i had installed the MDP, and wanted to keep it clear of the rif-raf, so i put a large piece of cardboard over it that read ;

Danger, 1000 Volts!

they all backed off, and all i heard was mumbles and grumbles about that sparky's higher than normal voltage!

Top
#112516 - 07/02/01 03:33 PM Re: Air Vents in Wireway
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Plumbers!
If you run into the character that did this on a job, replace his icemaker line for the refrig with a piece of bare #4 sol Cu. The fittings fit just perfectly, and it won't leak, even into the icemaker.
Plumbers!
Top
#112517 - 07/02/01 07:59 PM Re: Air Vents in Wireway
John Steinke Offline
Member
Registered: 04/03/01
Posts: 518
Loc: Reno,Nv., USA
Looks like a Darwin candidate was here! I'd like to know how he managed to avoid nicking any wires when he drilled- and how he killed the power!
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 43 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
KrmtFrg, Stack, Scotto, Freecrowder, clee512

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals