#112492 - 06/29/01 09:02 PM 200 - 225
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA

 Quote:
While getting some info for a single-line diagram I found this. Service is 277/480V, 1600A, with a number of 200A &1-400A Fusible Switches. The 400A was fused at 225A. OK. The first 200A Switch was fused at 225A . Huh? I really did a double take on this. The remaining 5- 200A were the same way.
Can you see how they managed this? What would/could happen if these units were called upon to "do their duty?"

Electure

Top
Tools for Electricians:
#112493 - 06/30/01 03:35 AM Re: 200 - 225
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
So U have 225A fuses in many 200A disco's. The result of a 'dead short' and subseqent AIC may see the disco, not the fuses, as the weak link.

Top
#112494 - 06/30/01 05:16 AM Re: 200 - 225
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
But the 225A 600V fuses in the 400A disco are way too large to fit in the 200A switch.

Top
#112495 - 06/30/01 08:00 AM Re: 200 - 225
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
yes they are, do you suppose there would also be more of a 'flashover' possibility???

Top
#112496 - 06/30/01 08:56 AM Re: 200 - 225
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I SURE DO see flashover as a problem. There was a hint in my last post, here's another, a little more obvious 110-4.

Top
#112497 - 06/30/01 11:55 AM Re: 200 - 225
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
no aurgement from me, we could list a few more codes on top of this. my post was stictly speculation, supposing a 'short', not G-fault across two phases fused side by side. they look close!
as a contractor, i find exercising that 'liability node' part of my grey matter to the worst case scenario essential to my survival it's a jungle out there!


Top
#112498 - 06/30/01 01:43 PM Re: 200 - 225
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
FRS>FRN, 480>250,(OK, I'll stop this secretive business). These are 250V rated fuses used on a 480V system. They actually fit sickeningly well into the fuse clips. We've included replacing these fuses with 200A, 600V fuses in our bid for the owners' work. If they don't want the work performed, they can't care much about their beautiful 4 story office building.

Top
#112499 - 06/30/01 02:41 PM Re: 200 - 225
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
pardon my ingnorance, now that U mention the obvious, they do look a tad short....


Top
#112500 - 07/01/01 07:32 AM Re: 200 - 225
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I sure hope you're not ignorant, Sparky, because I stood gawking, scratching my head, gawking some more for an awfully long time before I realized what was going on...and I could read the writing on the fuses!! We get so used to seeing things in a certain way that when something looks almost right, it almost passes us by. If you're ignorant, then I'm an absolute moron!

Top
#112501 - 07/01/01 08:02 AM Re: 200 - 225
sparky Offline
Member

Registered: 10/18/00
Posts: 5545
Ok, now that we have established the obvious, as applied to the original Q, what would happen if these fuses were called to duty?
In a worst case scenario ( all i can think of is a dead short), would we have the equivalent of 3 grenades?

Top