#112396 - 06/14/01 12:00 AM 2 Many Meters  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,434
NY, USA
[Linked Image]
Quote

The owner here wanted a price to add another 400 A meter & main to this service. When I told him he was in for some more work than that, (count 7 already) he became somewhat upset. Seems another "electrician" had just left after telling him he could "cut in" another.... right into the front of the utility pull box / landing lugs.(???) The customer thinks I'm full of it. (Like that clearance?)
I'm still laughing.

Electure



[This message has been edited by Webmaster (edited 06-14-2001).]


Tools for Electricians:

#112397 - 06/14/01 06:10 AM Re: 2 Many Meters  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
electure,
is the box to the left a main disco?


#112398 - 06/14/01 07:56 AM Re: 2 Many Meters  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
No, there is no main disconnect! That's the utility pull section. They'll have a can of worms opened soon. There are 3 buildings like this, each with 7 services.

[This message has been edited by electure (edited 06-14-2001).]


#112399 - 06/14/01 08:22 PM Re: 2 Many Meters  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
7????

seven???

as in the # after 6 ?

how could this be energized in the 1st place?
[Linked Image]

[This message has been edited by sparky (edited 06-14-2001).]


#112400 - 06/15/01 07:23 AM Re: 2 Many Meters  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
Yesiree, 7 as in 7. That's the #. Our price will include a Main switch, which will probably give the customer a coronary. I don't know how they got these things bought off, maybe the inspector's dog ate Article 230 from his book. I'll bet that the planner now, 30 yrs later, has a different view. (I still have the mental pic of the other guy, tracing around a 3 lb coffee can lid, and whipping out a jigsaw to cut a hole in the front of that pullsection for his new meter)...I'm still laughing.


#112401 - 06/15/01 07:58 AM Re: 2 Many Meters  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
I don't think that there is a violation here. 230-40 exception #1 permits one set of service entrance conductors for each occupancy. 230-71(a) permits 6 disconnects for each set of service entrance conductors.
Don(resqcapt19)


Don(resqcapt19)

#112402 - 06/15/01 05:34 PM Re: 2 Many Meters  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
would you guys be willing to get into 230-40, all the exceptions inparticular, a bit more ????


#112403 - 06/15/01 06:31 PM Re: 2 Many Meters  
sparky66wv  Offline
Member
Joined: Nov 2000
Posts: 2,232
West Virginia
Quote
I don't think that there is a violation here.


Other than the working clearances, I'll assume!! [Linked Image]


-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI

#112404 - 06/15/01 09:27 PM Re: 2 Many Meters  
electure  Offline


Member
Joined: Dec 2000
Posts: 4,259
Fullerton, CA USA
. 230-40,ex1 Service is 120/208
. " " ex2 Doesn't apply
. " " ex3 Doesn't apply
. " " ex4 Doesn't apply
. " " ex5 Doesn't apply
Ooops, I shouldn't have been in a '99 book. (There's a change) I still don't buy it, I believe the service point is at the landing lugs in the utility pullsection. From there the service entrance conductors can only have 6 disconnects.



[This message has been edited by electure (edited 06-15-2001).]


#112405 - 06/15/01 11:24 PM Re: 2 Many Meters  
resqcapt19  Offline
Member
Joined: Nov 2000
Posts: 2,148
IL
Electure
Quote
230-40: Exception No. 1: Buildings with one or more than one occupancy shall be permitted to have one set of service-entrance conductors for each class of service run to each occupancy or group of occupancies.


Each occupancy can have its own set of service conductors. If an occupancy requires more than one class of service it is permitted to have a set of service entrance conductors for ecah class of service. 240-71(a) says that each set of service conductors permitted by 240-30 Ex.#1 shall be permitted to have six disconnect switches. I'm assuming that each meter serves a seperate occupancy.

Sparky66,
Yes, I agree that there is a 110-26 violation here.

don(resqcapt19)


Don(resqcapt19)

Page 1 of 2 1 2

Member Spotlight
SafetyWired
SafetyWired
Pa, USA
Posts: 44
Joined: July 2013
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.017s Queries: 15 (0.004s) Memory: 0.8166 MB (Peak: 0.9898 MB) Zlib enabled. Server Time: 2017-03-24 02:13:23 UTC