#112366 - 06/01/01 06:56 PM Is an expansion fitting required here?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA

Photo submitted by Joe Tedesco
Quote:
Question: Is an expansion fitting required here?
Top
Tools for Electricians:
#112367 - 06/02/01 11:58 AM Re: Is an expansion fitting required here?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
The answer to this is easier to find in the '99 NEC than the '96. The table for the expansion of PVC has been moved to Article 347 from an obscure spot in Chapter 9.
­ If that conduit is 4' long, and the temperature change is 130°, the answer would be no. (5.3"X.04=.212", which is less than 1/4")
However, if it's 5' long, with a 130° change in temp,5.3"X.05=.265", one would be required.
Top
#112368 - 06/02/01 02:43 PM Re: Is an expansion fitting required here?
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Temperatures not withstanding, if frost heave is a problem, then an expansion fitting would be required. Look in the misc. section of the code, 300-5(j)

Tom
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top
#112369 - 06/02/01 02:55 PM Re: Is an expansion fitting required here?
Anonymous
Unregistered

I wouldn't expect frost to be a problem if the conduit extends below the frost line.

The temperature change of the portion below ground is narrower.

Frost can heave inches in certain soils. A simple expansion joint won't solve that problem.
Top
#112370 - 06/02/01 02:55 PM Re: Is an expansion fitting required here?
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Thanks, I never thought about that, being from So.CA. That's one thing that's so good about the BB, is that I'm able to learn about circumstances and reasons for other locations. (Is this what you guys were calling a "frosty"?) I just thought of the 130° as being a pretty extreme variance
Top
#112371 - 06/02/01 07:13 PM Re: Is an expansion fitting required here?
golf junkie Offline
Member
Registered: 04/22/01
Posts: 507
Loc: York, NE
With the last code review our AHJ decided that all transitions from above or below grade must have expansion fittings. I have had to pull a direct buried service lateral and install a expansion joint when the pipe ended 18" below grade.

I agree that the expansion joint is a good idea when running continuos conduit.....but when direct burial is used, it's ridiculous

GJ
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 93 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals