#112334 - 05/27/01 08:34 AM What's Wrong Here?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA


Give the rules in the NEC that can be used to cite the violation here.
_________________________
Joe Tedesco, NEC Consultant
Top
Tools for Electricians:
#112335 - 05/28/01 06:53 PM Re: What's Wrong Here?
Glenn Offline
Member
Registered: 01/17/01
Posts: 75
410-57(b)

Glenn
Top
#112336 - 05/29/01 09:26 AM Re: What's Wrong Here?
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA
410-57(b) Wet Locations.

1. A receptacle installed in a wet location where the product intended to be plugged into it is not attended while in use (e.g., sprinkler system controllers, landscape lighting, holiday lights, etc.) shall have an enclosure that is weatherproof with the attachment plug cap inserted or removed.
_________________________
Joe Tedesco, NEC Consultant
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 11 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals