ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#112213 - 04/27/01 08:56 PM A Killer Setup here!
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA


Submitted by Electure
Quote:
Your normal stuff. 2 wires w/strands cut off in each lug, etc. (that CØ load wire is gray). with a special twist on this installation. There were 4 individual saws and a dustcollector connected, each with its own EXO & Mag Starter. The T1 terminals in the mags of all the saws were jumpered together, and 1 wire was run to the coil of the duster's mag to make it run when any saw was turned on, (other side of 480 coil went to line in duster mag)
Bottom Line: You turned off a disconnect to change a motor. You tested the power & it was off. While your working, someone turned on another saw 100' away, and your AØ motor lead was instantly 277 to ground, because it was being fed by a totally different source. You never got a chance to figure out what happened.
(but fortunately we fixed it first)
Top
Tools for Electricians:
#112214 - 04/27/01 09:01 PM Re: A Killer Setup here!
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
Wow! How did you manage to discover this the easy way... sans funeral. I guess opening up this "pandora's box" was enough to raise suspicion!
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
#112215 - 04/28/01 04:10 AM Re: A Killer Setup here!
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
There was a 3/4" conduit that ran the length of the installation for the control. It only had 1 pink #14 in it. Red Flag went up.
We built the building for this Lumberyard/ Homecenter in '97, they had their "Millwrong"(nothing right about him) do the machinery work after we left.
Top
#112216 - 04/28/01 11:15 AM Re: A Killer Setup here!
Tom Offline
Member
Registered: 01/01/01
Posts: 1044
Loc: Shinnston, WV USA
Nice save! Of your life that is. This is another example of "if it works, it must be OK."

What is it about woodworking and or sawmills? Around here, 9 out of 10 have some serious problems. The 2 favorite tricks are: using green for a phase conductor on 480 and since 480 panelboards are more expensive, using a 120/240 panelboard on a 480 system.

Tom

[This message has been edited by Tom (edited 04-28-2001).]
_________________________
Few things are harder to put up with than the annoyance of a good example.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 51 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals