The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!


2017 NEC and Related
2017 NEC
Now Available!

Recent Posts
Parking lot pole light swap....
by gfretwell
Yesterday at 08:46 PM
International Wire Colour Codes
by Tjia1981
10/23/16 12:08 PM
Son of Sparky
by HotLine1
10/20/16 07:43 PM
Speaking of Plugmold ...
by gfretwell
10/17/16 02:37 PM
Broken battery charger? Check for cobwebs!
by gfretwell
10/17/16 02:30 PM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 14
HotLine1 7
ghost307 7
renosteinke 6
Potseal 4
Who's Online
1 registered (Tjia1981), 278 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#11147 - 07/01/02 09:10 PM 38.4 kHz
Tom Baker Offline

Registered: 10/09/01
Posts: 31
Loc: Bremerton WA
I am reviewing the use of an "In-Roadway lighting" system which is typically used at crosswalks. Many of these systems operate at 12 VDC, 3 amps, with LED lamps, operating from wires placed in a sawcut in the road surface. These systems are fairly safe, being similar to low voltage landscape lighting.

One system operates at 38.4 kHz, about 30 volts, perhaps 4 amps. The LED lamps are inductively powered from the cable.

I'm trying to determine what the shock hazard at 38.4 kHz would be. any comments or suggestions on where to look?

Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#11148 - 07/02/02 11:44 AM Re: 38.4 kHz
pauluk Offline

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England

I don't think 38kHz poses any more of a shock hazard than 50/60Hz or the same voltage.

In fact, I remember reading somewhere in the past the normal 50 or 60Hz power frequencies are actually just in the critical range which is most likely to cause ventricular fibrillation. I'm not sure what to start looking to confirm that, though.