#111153 - 09/08/06 04:17 AM Not Spectacular
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
No smoke, no fire.
I had to test the photocell, and just happened to open the box. The bottom conduits run underground to an ATM machine about 100' away. All the power circuits are 120V.
How many violations are there here?




(BTW, this job passed inspection)

[This message has been edited by electure (edited 09-08-2006).]

Top
2014 / 2011 NEC & Related Books and Study Guides
#111154 - 09/08/06 08:17 AM Re: Not Spectacular
techgod Offline
Member

Registered: 12/15/03
Posts: 20
Loc: Burbank, Ca USA
At least the installer maintained the minimum bending radius for the Cat 5.
_________________________
Mark Stetson
Stetson Electric

Top
#111155 - 09/08/06 11:08 AM Re: Not Spectacular
LarryC Offline
Member

Registered: 07/05/04
Posts: 776
Loc: Winchester, NH, US
I like the Cheshire cat neutral coming out of the wire nut. (Slowly fades away until nothing is left)

Larry

Top
#111156 - 09/08/06 02:23 PM Re: Not Spectacular
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Larry the white that 'vanishes' actually dives down the left hand 1/2".

Looks like a hex head Tek screw holding the grounding lug.

The paint was not cleaned off at the grounding lug.

There are two conductors in a terminal that is rated for one (IMO)

The neutrals look less than 6"

That group of funny blue cables might be better off in a separate enclosure.

And it's missing the cover.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#111157 - 09/08/06 05:27 PM Re: Not Spectacular
CaOperator Offline
Member

Registered: 04/17/03
Posts: 56
Loc: Los Angeles, CA, USA
Oops just reread, the post, it is a photocell, lol.


[This message has been edited by CaOperator (edited 09-08-2006).]