#110973 - 08/14/06 08:41 PM Service in Garage
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Some people just don't think ahead. The general contractors must be smoking something.

Alan Nadon




Top
2017 / 2014 NEC & Related Books and Study Guides
#110974 - 08/14/06 09:36 PM Re: Service in Garage
Larry Fine Offline
Member
Registered: 02/18/05
Posts: 693
Loc: Richmond, VA
It looks more like a carport, with no garage door. Still...
_________________________
Larry Fine
Fine Electric Co.
fineelectricco.com
Top
#110975 - 08/15/06 02:34 PM Re: Service in Garage
Celtic Offline
Member
Registered: 02/26/05
Posts: 361
Loc: NJ
Spontaneous Construction!
_________________________
~~ CELTIC ~~
...-= NJ =-...
Top
#110976 - 08/15/06 05:08 PM Re: Service in Garage
Check Pilot Offline
Member
Registered: 11/25/05
Posts: 141
Loc: Edmonton Alberta Canada
What kind of nutbar deal is this? Must be a real crowd pleaser when the meter readers come along. And what's with the cock-eyed light by the inside door? Roof too low or the light couldn't be moved down?
Top
#110977 - 08/16/06 05:53 PM Re: Service in Garage
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
I got a few of these up here in 'Jersey'. Usually an un-permitted car port close-in. Interesting that the roof & siding show no signs of 'addition' work.

The leaning fixture was/is probably something that was on the 'Honeydo' list.

John
_________________________
John
Top
#110978 - 08/17/06 04:14 AM Re: Service in Garage
SteveFehr Offline
Member
Registered: 03/19/05
Posts: 1195
Loc: Chesapeake, VA
With the advent of remote readers, will accessibility of the meter be a non-issue in the future? (I mean with regards to locked doors and meter reading, not cramped closets and servicibility.)

I can certainly empathize with the homeowner here- they obviously didn't sink much money into that garage, and I doubt they could have afforded to move that meter. Then you get into other NEC issues regarding restriction on SE length and placement of the panel, and all of the sudden, the homeowner has $10k worth of electrical work for a $500 DIY job. Would be so easy to just ignore the problem, especially if you didn't even realize it WAS a problem. In fact, knowing how expensive the problem is, I'd probably have done the exact same thing...
Top
#110979 - 08/17/06 05:14 PM Re: Service in Garage
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Agreed, it's costly to relocate the service. but.......I'll play devils advocate.

Unprotected (service) conductors within the structure??

Also, how about the pressure vent gizmo on the gas meter??? Nothing like dumping into the structure!

Les: (LK) what do you say? ever seen one of these??

John
_________________________
John
Top
#110980 - 08/17/06 06:15 PM Re: Service in Garage
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Seriously... how much would anyone charge to do that the right way??? Yank the old meter off the wall, 6X6X4 NEMA 1 pullcan, maybe 30' 1½" EMT and 40'X 3 #2THHN, and a meter/main breaker can (to eliminate the unfused feeder situation) landed on the side of the new garage a couple ground rods and 15' #6 AC and this would be good to go Hell, you could probably salvage the old riser and feeders if they were really that hard up (I cant tell what condition they're in)
(This garage looks tiny, like Stuart Little might park there )

PS. get the lazy phone guy to stop tying to our risers!
Top
#110981 - 08/17/06 09:29 PM Re: Service in Garage
LK Offline
Member
Registered: 01/21/03
Posts: 1429
Loc: New Jersey
"Unprotected (service) conductors within the structure??"

Another one of those don't worry about the permit jobs, i bet the guy that did it, still thinks he knew what he's doing, the gas vent is good where it is, all the evidence will be gone, the first time the vent dumps!

That job will end up costing them, when they try to sell.
Top
#110982 - 08/18/06 05:31 PM Re: Service in Garage
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
OK, I had 1 of these today. relocated to the left garage wall.

200 amp PSE&G pan; 200 amp rated service
2-1/2" RGC mast, boot, guy wire
200 amp CB main, 3R
40' SER to existing panel.
2 rods; jump water meter & water heater.
80' #4 to street side water main

Job Cost (on permit) $1675.00

John


[This message has been edited by HotLine1 (edited 11-16-2006).]
_________________________
John
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (annemarie1), 67 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals