ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#110894 - 07/25/06 09:08 PM Bulbs Above Ceiling
Admin Online   content

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Home owner decided to install a drop ceiling and wanted the soft glow of lights above the cloth material that he used. Fortunately he was stopped before the soft glow became an open flame.

Alan Nadon
Top
2017 / 2014 NEC & Related Books and Study Guides
#110895 - 07/26/06 04:47 AM Re: Bulbs Above Ceiling
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
Alan,
Who determines the distance required from an incandescent bulb to combustibles? I'm not familiar with an easy referenced code to indicate a violation. I have a wall sconce that is sometimes very close to the curtains (depending on the position of the curtain), but I'm not sure it's a violation.
_________________________
Ron
Top
#110896 - 07/26/06 04:58 AM Re: Bulbs Above Ceiling
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Ron,
Does it have to be an electrical violation to constitute disconnecting a thing like this?.
Common-sense would tell me that a thing like this can only end in tears.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#110897 - 07/26/06 11:24 AM Re: Bulbs Above Ceiling
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
I would think the use of open-cleat lampholders, what appears to be zip cord and the nice flying splice from the ceiling box is more than enough to warrant the red sticker. Plenty of electrical reasons for a disconnect here.

And since there is always the possibility of one of those incand. bulbs shattering and dropping hot glass and maybe sparks on the cloth, come on. What more do you need?

A better solution would be an enclosed luminare, wired with proper methods and preferably flourescent. That would give the desired effect with minimal or no hazards.

edited to add:

And last time I checked, open cleat lampholders were hard to get and somewhat pricy. It probably would have cost less to do it right anyway.

[This message has been edited by mxslick (edited 07-26-2006).]
_________________________
Stupid should be painful.
Top
#110898 - 07/26/06 11:37 AM Re: Bulbs Above Ceiling
energy7 Offline
Member
Registered: 06/10/02
Posts: 58
Loc: Oxnard, CA, USA
Regarding the clearance issue, the closet code section (2002 - art. 410.8) would probably be a good place to start.
Aren't the distances specified because of "distance to combustibles" and "protection from physical damage" issues?
Top
#110899 - 07/26/06 03:05 PM Re: Bulbs Above Ceiling
Ron Offline
Member
Registered: 03/13/02
Posts: 582
Loc: White Plains, NY
I'm not saying that the installation method is a good one, I'm suggesting that a keyless lampholder doesn't seem to be a violation. I was not able to see the zip cord or the splice without a box. Clearly those violations should be tagged, but the lampholder itself .... I'm not sure that is a technical violation of the NEC. That area is not a closet.
_________________________
Ron
Top
#110900 - 07/27/06 03:41 AM Re: Bulbs Above Ceiling
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
I claim that light installation (or at least the stuff used) is close to 100 years old! That's twisted cloth lamp cord! That stuff belongs into a museum!
Top
#110901 - 07/27/06 06:42 AM Re: Bulbs Above Ceiling
mamills Offline
Member
Registered: 11/30/01
Posts: 745
Loc: Wharton, Texas, USA
Ranger: As strange as it may sound, that stuff is still available here. Our city recently completed a full remodeling/rebuilding project of a turn of the century railroad depot (the last century, that is ). The electrical system in the building was completely replaced, but the lighting fixtures throughout consist of the traditional (for that time) bare light bulbs in new brass sockets hanging from the 12' high ceilings with that twisted cloth covered rubber "drop cord" stuff. Really strange in a remodel where everything alse is completely code compliant - boxes, conduit, receptacles, circuit breakers, etc.

They were going for "atmosphere", I guess...

Mike (mamills)

[This message has been edited by mamills (edited 07-27-2006).]
Top
#110902 - 07/28/06 04:25 AM Re: Bulbs Above Ceiling
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
Yeah, you still get it here too, but the price is _real_ steep! So with that kind of job I'd guess old work.
Top
#110903 - 07/28/06 12:20 PM Re: Bulbs Above Ceiling
Alan Nadon Offline
Member
Registered: 03/10/05
Posts: 399
Loc: Elkhart, IN. USA
Check NEC 2005 Section 110.3 (A) 5
Lampholders are not luminaires or else 410.65 would be the place to start.
Alan--
_________________________
Alan--
If it was easy, anyone could do it.
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals