#110436 - 04/10/06 04:52 PM An Emergency Panel
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
This panelboard powers the lighting in the stairs and corridors, the exit fixtures, etc in a 9 story residential building.

In an outage, the 480V generator will power this panel through a little 30 KVA transformer.

And then..............?






Top
2014 / 2011 NEC & Related Books and Study Guides
#110437 - 04/10/06 05:05 PM Re: An Emergency Panel
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Well Scott,
That transformer will work.... for a short time at least.
How could a thing like this happen?.
One other thing, I have certain mis-givings about that run of EMT over the top of that exhaust silencer as well, we all know how hot they get!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#110438 - 04/11/06 08:55 PM Re: An Emergency Panel
mhulbert Offline
Member

Registered: 10/19/04
Posts: 133
Loc: Anaheim, CA USA
What exactly is wrong here...I thought the panel was not fed, but on closer look it seems there is a feeder coming in the bottom of what looks like a feed trhough panel.

Am I missing something stupidly obvious?

mike

Top
#110439 - 04/12/06 03:44 AM Re: An Emergency Panel
George Corron Offline
Member

Registered: 05/16/01
Posts: 728
Loc: Lorton, Va USA
Agreed, more info is needed here. Many of those 'silencers' (they're not called mufflers for a reason) are wrapped inside with fire and heat retardent. That means it may not get as hot as you'd think, but that should be in the submittal documents. It also appears that it was here for some time prior to the EMT, so who's problem is that?

I'd be more concerned with the "air over" portion of the cooling. That's something that will get overlooked over the years.

Top
#110440 - 04/12/06 04:06 AM Re: An Emergency Panel
IanR Offline
Member

Registered: 12/06/04
Posts: 326
Loc: Palm Bay FL USA
"the 480V generator will power this panel through a little 30 KVA transformer.

And then..............?"

While a 30KVA transformer looks a little undersized for the generator. (I am guessing by the 6cyl diesel that it is 60KW or more)
If it has a correctly sized OCD it should be fine electrically. No doubt the diesel will wet stackfrom being underloaded, but that is another story. Outside of the EMT over the exhaust, I don't see too much problem.
Well, I don't see any fire suppression system either, but that could just be outside of the photo.

Top
#110441 - 04/12/06 05:14 AM Re: An Emergency Panel
n1ist Offline
Member

Registered: 02/13/02
Posts: 176
Loc: Malden MA
30KVA for 9 stories is about 3KVA/floor. Depending on the size of each floor and types of fixtures on emergency power, that may be enough.

Top
#110442 - 04/12/06 09:54 AM Re: An Emergency Panel
T-Kat Offline
Junior Member

Registered: 12/10/04
Posts: 4
Loc: Morristown,Tenn. USA
Since this is a lighting and appliance panel,408.36(D) requires overcurrent protection on the secondary side of the transformer. I don't see a main breaker or any other OCP device in the picture.

Top
#110443 - 04/13/06 02:07 AM Re: An Emergency Panel
techie Offline
Member

Registered: 05/17/05
Posts: 240
Loc: palo alto, ca usa
I would assume that the generator is powering more than just lighting, otherwise why would it be a 480v genset?

Top
#110444 - 04/13/06 04:37 AM Re: An Emergency Panel
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Sorry it took me so long to get back to this.

The 30 KVA is plenty to supply the loads that are fed here. My big concern is with the 1" EMT run right above the silencer.

This is not the original panel that was installed, it was installed, I believe, after this one about 10' away burnt out, . (And probably without a permit or inspection)



There's lots of heat coming off of that exhaust system. This has happened just during weekly tests of about 15 minutes.



Also, the panel is mounted right under the silencer's drain plug.

The 480V genset does supply other loads, but has enough capacity to handle them.

Top
#110445 - 05/02/06 03:09 PM Re: An Emergency Panel
Gus99 Offline
Member

Registered: 08/11/05
Posts: 26
Loc: Los Angeles, CA
9 story building? 480v generator?

Can you say "elevator machinery"

Top