ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

Topic Options
Rate This Topic
#109706 - 11/24/05 05:26 AM Blank as Panel Part
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Forwarded by Joe Tedesco:

Quote:
Joe, my apprentice in my second year class came across this situation where a 4 square blank cover was used in a piece of
electrical
switchgear to support a 480 volt breaker to the bus.



Top
2017 / 2014 NEC & Related Books and Study Guides
#109707 - 11/24/05 06:06 AM Re: Blank as Panel Part
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
It looks fine to me.

It is simply a bracket to hold the tail end of a breaker, it does not carry current or provide a fault path it is most likely stronger than the factory part.

I would have ordered the correct part but if I was in a panel and saw this I would not worry about it or recommend it be replaced.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#109708 - 11/24/05 05:14 PM Re: Blank as Panel Part
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
Blank covers are pretty thick metal. I wonder how he made that offset bend?
_________________________
John
Top
#109709 - 11/24/05 08:18 PM Re: Blank as Panel Part
NORCAL Offline
Member
Registered: 09/25/02
Posts: 865
If they had a brake around, no problem to bend cover.
Top
#109710 - 11/25/05 12:48 AM Re: Blank as Panel Part
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
"support a 480 volt breaker to the bus"?

Was this an actuall electrical connection? If so, no way!

Non current carrying support, hmmm OK....
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#109711 - 11/25/05 11:58 AM Re: Blank as Panel Part
PCBelarge Offline
Member
Registered: 06/08/03
Posts: 681
Loc: Dobbs Ferry, NY, USA
I do not see how this is okay at all???????

Professionals find a way to make it work, but not this way. Isn't that why we are professionals? It physically works, but this is not right. Supply houses and manufacturers are in business to supply this type of material, so we can get it done............OH WAIT.... we don't have the time to do it with the proper material, lets see, HMMMMMM,lets see what we can do to make it work.


This is a problem with the "culture" of our industry. It works, so it is okay... and we wonder why it is so hard to try and raise our industry back up to where it should be.

And the guy who does want to do it properly will have a hard time convincing the customer that it has to be done properly, as the next guy is ready to do it CHEAP & QUICK.

I can see how this culture change is going to be an uphill battle for quite some time to be.
_________________________
Pierre Belarge
Top
#109712 - 11/25/05 12:12 PM Re: Blank as Panel Part
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Under a bolted fault condition would those 2 button head screws be enough to hold that breaker tight if things started "jumping around"? I could see this for a temp fix maybe, but I'd certainly seek out the proper mounting hardware to keep things within UL specs...

Was the breaker even designed for the gear it was installed with?

Randy
Top
#109713 - 11/25/05 12:20 PM Re: Blank as Panel Part
renosteinke Offline
Cat Servant
Member
Registered: 01/22/05
Posts: 5316
Loc: Blue Collar Country
Funny...I was just working on some gear that looked like that.

In my task, I was hindered by the little detail that the maker had stopped making his Fine Pieces of Engineering. While I was able to locate the breakers I needed, I was not able to obtain the necessary hardware.
So, in my case, I spent a pile of money having a machine shop duplicate existing hardware. Not only did I need plates like the one fabricated here, I needed aluminum standards for connecting the breaker to the busses.

This gear, btw, had 1/4-20 bolts as the typical connectors.

[This message has been edited by renosteinke (edited 11-25-2005).]

[This message has been edited by renosteinke (edited 11-25-2005).]
Top
#109714 - 11/27/05 09:58 AM Re: Blank as Panel Part
e57 Offline
Member
Registered: 05/27/03
Posts: 2876
Loc: S.F.,CA USA
"Non current carrying support, [begrudging]hmmm OK...."

Personally, I would have a part remanufactured if no longer made by the original manufacturer. There are places I could attempt to locate original parts as well. And a shop I can get anything I want made, and they often have factory drawings for the equipment parts.

If it were a current carrying part... This would not be acceptable! Non-current carrying, I wouldn't do it, but don't see this a danger.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason
Top
#109715 - 11/27/05 12:23 PM Re: Blank as Panel Part
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
Don't like this at all. Too sloppy and despite the thickness of the blank, inadequate mounting by those tiny screws.

In reality I would be far more concerned by all the metal shavings on that bottom rail!
_________________________
Stupid should be painful.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 90 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals