#109656 - 11/17/05 06:33 PM How'd This Happen?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
One of the guys was unscrewing a blank cover on a different box about 100' away when he heard the pop inside the box he was working on. The screw had apparently rubbed a conductor raw inside.

The simultaneous sound of this one kind of made it hard to hear, though.








Top
2014 / 2011 NEC & Related Books and Study Guides
#109657 - 11/17/05 06:52 PM Re: How'd This Happen?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Just a guess that one of the switches was not happy with the available fault current.

That is really ugly.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#109658 - 11/17/05 07:22 PM Re: How'd This Happen?
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Scott,
What make/brand switches are those?.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#109659 - 11/17/05 07:54 PM Re: How'd This Happen?
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
i am sure it look like Hubbel 2 pole switch but the Pass & Syemour look very simuir too but i am not too sure about Levetion they look little diffrent

i can tell this was wired up on 277/480 volt circuit

if running more than 300 volts it should have " divider " on there and i dont see any of it in the switch box at all.

the other thing i can see that the switch is allready wired on 480 volts so that get more spooky there

Merci, Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#109660 - 11/17/05 09:15 PM Re: How'd This Happen?
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
Were these 4ways or 2pole switches? If they're 2 pole, and there was 480V being run through these, the fault downstream (I'm assuming) probably found its weakest link being the switch contacts not being rated for the fault voltage.. But you say a faceplate screw caused the fault which would be at 277V if all was grounded properly, or did more than one wire get damaged?

The switches are Hubbell, you can make out their oval insignia above the toggles on the yokes...

Top
#109661 - 11/18/05 04:26 AM Re: How'd This Happen?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Yup, Marc's right. (I told the answer on the chat, which may have helped )
2 Poles, Hubbell, with a label on the side "2 Pole for single circuit only".

The installer chose to disregard the label, and ran 480V through them. The fault was 277V, caused by 8-32 in the corner of a 4-S box. The switch on the left took the fault, and its failure sent this "Jack and the Beanstalk" effect into high gear.

There were 18 of these switches installed (that's 36 circuits). The customer had me remove all of them
They will be replaced with contactors.
(BTW, None of the 20 Amp breakers tripped)



[This message has been edited by electure (edited 11-18-2005).]

Top
#109662 - 02/02/07 04:02 PM Re: How'd This Happen?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA


Here's what I found instead of contactors when I happened by the place again.





Now what ??

[This message has been edited by electure (edited 02-02-2007).]

Top
#109663 - 02/02/07 04:33 PM Re: How'd This Happen?
Theelectrikid Offline
Member

Registered: 04/30/04
Posts: 854
Loc: Levittown, PA
Where's that rolleyes smiley, wait, here it is!

Whaddaya expect? Someone to spend money replacing the old switches with new contactors?

(BTW Scott, no cursing. )

Ian A.

[This message has been edited by Theelectrikid (edited 02-02-2007).]
_________________________
Is there anyone on board who knows how to fly a plane?

Top
#109664 - 02/03/07 03:48 AM Re: How'd This Happen?
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
To quote a character from an old British movie about a couple fixing up an old house (including wiring):

"They never learn!"

Top
#109665 - 02/03/07 07:16 AM Re: How'd This Happen?
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
I wonder if this is why the code wants dividers for >300V.. to block the shrapnel from the other switches.

I have an old GE 3P toggle switch rated 20A 600V if they're really against the contactors, they might want to look into them. I'm sure they're not cheap though. Here are the ones from P&S..

edited to fix link