#109528 - 10/30/05 09:10 PM Kitchen Receptacle
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Picture submitted by royal12136:

Quote:
What code does this violate?


_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
2017 / 2014 NEC & Related Books and Study Guides
#109529 - 10/31/05 01:32 PM Re: Kitchen Receptacle
mxslick Offline
Member
Registered: 10/24/04
Posts: 803
Loc: Atomic City, ID USA
First off, I'd cite 210-52(c)(5), as this is not located in a readily accessable spot.

Also 210-8(a)(6), GFI protection for kitchens.

Can 110-12 apply here as well?

(All above from '99 NEC)
_________________________
Stupid should be painful.
Top
#109530 - 10/31/05 02:23 PM Re: Kitchen Receptacle
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
One question Tim,
Has that Duplex been sawn off to fit above the bench?.
It's just that the splash-back looks awfully close to the wall.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#109531 - 10/31/05 03:27 PM Re: Kitchen Receptacle
electure Offline


Member
Registered: 12/24/00
Posts: 4259
Loc: Fullerton, CA USA
Looks to me like the backsplash is a recent addition.

The duplex might have been there for a long time, and if it was installed previous to the requirement for GFCI protection, it is not a violation, although a suggestioncould be made to add the protection. It also could be a downstream device from a GFI receptacle or C/B.

Looks like it's time to take a chain saw to the backsplash, and let the countertop guy fix the results
Top
#109532 - 10/31/05 04:03 PM Re: Kitchen Receptacle
royal12136 Offline
Member
Registered: 10/29/05
Posts: 20
Loc: Shasta Lake, CA USA
As far as I can tell, the receptacle has been cut off at the top of the backsplash. The countertop was installed in the 70's and there is no gfi's in the house. As it is I have found only one circuit with a ground.
I plan on trying to remove the receptacle this coming weekend when I have more time.
Thanks for the responses.
Tim
Top
#109533 - 10/31/05 04:55 PM Re: Kitchen Receptacle
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Thank the Lord for that,
So my eyesight isn't as poor as first thought!.
Mind you, that's not a "field-modification" I'd like to see catch on.
It's anyones guess what's behind that splash-back then!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#109534 - 11/01/05 02:47 PM Re: Kitchen Receptacle
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Other than gfi protection, if that counter is not secured no violation.
Top
#109535 - 11/01/05 04:50 PM Re: Kitchen Receptacle
wa2ise Offline
Member
Registered: 11/29/02
Posts: 782
Loc: Oradell NJ USA
Quote:
if that counter is not secured


The plumbing pipes connected to the sink probably makes that counter not movable, so in a sense it's secured. Presumidly that box could be rotated and mounted sideways to allow full access to both outlets per code.
Top
#109536 - 11/01/05 05:23 PM Re: Kitchen Receptacle
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
What is the requirement for full access to both outlets?
Top
#109537 - 11/02/05 05:09 AM Re: Kitchen Receptacle
n1ist Offline
Member
Registered: 02/13/02
Posts: 183
Loc: Malden MA
How about the requirement for the box itself to be accessible?
Top
Page 1 of 3 1 2 3 >

Member Spotlight
Member Since: 10/07/00
Posts: 3417
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 35 Guests and 9 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals