#109125 - 10/24/03 08:48 PM Water Pipe Location
Admin Online   content

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
Is it a violation for a water pipe to be under the equipment here?

Joe
Top
2017 / 2014 NEC & Related Books and Study Guides
#109126 - 10/25/03 08:49 AM Re: Water Pipe Location
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
While there is not a violation of the safety work space required by 110.26(A), there is a violation of the "dedicated equipment space" required by 110.25(F)(1)(a).
Don
_________________________
Don(resqcapt19)
Top
#109127 - 10/25/03 01:31 PM Re: Water Pipe Location
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I am wondering about what looks like the use of parallel conductors smaller than 1/0?

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#109128 - 10/25/03 05:21 PM Re: Water Pipe Location
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Quote:
Is it a violation for a water pipe to be under the equipment here?


Or is the violation having the equipment over the water pipe?
Top
#109129 - 10/28/03 04:55 PM Re: Water Pipe Location
mvpmaintman Offline
Member
Registered: 09/15/03
Posts: 123
Loc: Manhattan, Kansas, USA
I think a bigger problem might be the pipe above the panel from the looks of the rust on the outside of the panel and the trough under it. I popped a cover on one like this once and found two of the three fuses in the main rusted into the holders.
Top
#109130 - 10/30/03 08:37 PM Re: Water Pipe Location
Knightelectrical Offline
Junior Member
Registered: 10/29/03
Posts: 3
Loc: Germanton,NC USA
Lots of problems here. Are those the right kind of straps, look like one hole EMT straps to me.
334.15 B (NM cable?) "shall be protected" is not met.
Top

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 36 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals