#109125 - 10/24/03 08:48 PM Water Pipe Location
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
Is it a violation for a water pipe to be under the equipment here?

Joe

Top
2014 / 2011 NEC & Related Books and Study Guides
#109126 - 10/25/03 08:49 AM Re: Water Pipe Location
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
While there is not a violation of the safety work space required by 110.26(A), there is a violation of the "dedicated equipment space" required by 110.25(F)(1)(a).
Don
_________________________
Don(resqcapt19)

Top
#109127 - 10/25/03 01:31 PM Re: Water Pipe Location
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
I am wondering about what looks like the use of parallel conductors smaller than 1/0?

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#109128 - 10/25/03 05:21 PM Re: Water Pipe Location
ThinkGood Offline
Member

Registered: 08/07/02
Posts: 1084
Loc: Milwaukee, WI
 Quote:
Is it a violation for a water pipe to be under the equipment here?


Or is the violation having the equipment over the water pipe?

Top
#109129 - 10/28/03 04:55 PM Re: Water Pipe Location
mvpmaintman Offline
Member

Registered: 09/15/03
Posts: 113
Loc: Manhattan, Kansas, USA
I think a bigger problem might be the pipe above the panel from the looks of the rust on the outside of the panel and the trough under it. I popped a cover on one like this once and found two of the three fuses in the main rusted into the holders.

Top
#109130 - 10/30/03 08:37 PM Re: Water Pipe Location
Knightelectrical Offline
Junior Member

Registered: 10/29/03
Posts: 2
Loc: Germanton,NC USA
Lots of problems here. Are those the right kind of straps, look like one hole EMT straps to me.
334.15 B (NM cable?) "shall be protected" is not met.

Top