#109073 - 11/07/03 08:58 PM Service Violation
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
This is a 200A OH service, there is a visible violation, with a rusty noodle in the panel due to it, probably old hat to the ECN crew and those whom do 'dripping' panel' service calls...

~Steve aka sparky~
Top
2017 / 2014 NEC & Related Books and Study Guides
#109074 - 11/08/03 03:52 AM Re: Service Violation
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Certainly a violation of 230.54 (C). A better drip loop would also fix the problem.(The violation would remain however) Also the weatherhead should not be angled like that.

[This message has been edited by Electricmanscott (edited 11-08-2003).]
Top
#109075 - 11/09/03 02:35 AM Re: Service Violation
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I've taken to stuffing my weatherheads with dux seal in the last few years, as a hedge to noodlitis....
Top
#109076 - 11/09/03 08:04 PM Re: Service Violation
Bill Addiss Offline
Member
Registered: 10/07/00
Posts: 3875
Loc: NY, USA
Sparky,

Just curious here, in the Meter enclosures you use now is the Neutral connection in the middle?

The reason I ask is the ones we use now for the last couple of years have the Neutral connection moved to the left side and out of the central 'drip-zone'

Bill
Top

Member Spotlight
Member Since: 08/22/05
Posts: 44
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 30 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Scotto, Freecrowder, clee512, Jdscott2005, FAIZAN

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals