#108298 - 05/13/04 08:51 PM Outdoor Violation Photos
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
I took these photos when investigating problems with some outdoor receptacles. Apparently someone installed the Romex to bypass a defective run of UF cable. The photos reveal many violations.

- electricman2






(submitted via Joe Tedesco)
Top
2017 / 2014 NEC & Related Books and Study Guides
#108299 - 05/13/04 11:12 PM Re: Outdoor Violation Photos
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Is it just me, or does this whole installation look like something that was meant to be "temporary" sometime around oh,....1978?? I think I'm seeing NM-B coming from the PVC conduit in the first pic also! Seeing that this is obviously along a street also, I should assume the deadfront is missing from the subpanel? No ground bar, open KO's, missing parts, Romex outdoors, open J boxes...All out in public? Someone's looking to get sued! even arrested depending on what state this is!
Electricman2, the responsible party(ies) are letting you fix this crap, I hope!?!!

-Randy

PS... Bet $1 that the original UF cable was less than 8 inches underground!

-
Top
#108300 - 05/14/04 04:26 PM Re: Outdoor Violation Photos
Ryan_J Offline
Moderator
Registered: 08/19/03
Posts: 1374
Loc: West Jordan, Utah, USA
It looks like yellow 12 AWG NM cable, which makes me think this wasinstalled in the last year or two. ::mad

[This message has been edited by Ryan_J (edited 05-14-2004).]
_________________________
Ryan Jackson,
Salt Lake City
Top
#108301 - 05/14/04 04:26 PM Re: Outdoor Violation Photos
Trumpy Offline


Member
Registered: 07/05/02
Posts: 8211
Loc: SI,New Zealand
Man!.
Someone was in a hurry when they done this job.
It just screams of poor quality.
Randy,
I think you may have won that bet.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin
Top
#108302 - 05/14/04 05:21 PM Re: Outdoor Violation Photos
electricman2 Offline
Member
Registered: 11/09/03
Posts: 269
Loc: Thomasville, NC USA
The yellow cable is indeed NMB Romex. It is buried for about 15 feet from the panel to the box in pic 1. There are 5 of these boxes with receptacles to serve vendors equipment during street festivals etc. All of them are in bad condition, device screws broken or missing, broken covers etc. Randy mentioned no ground bar. This is service equipment. The meter can is above the panel out of the picture. Also I removed the deadfront to take the picture. I am going to suggest they remove the whole thing and start over. This is one of those situations where "temporary" quipment became permanent
_________________________
John
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
2 registered (gfretwell, sparkyinak), 53 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals