#108120 - 06/02/04 05:24 PM What's Wrong?
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
I don't know any of the history behind this, but thought it would make a good addition to the board.
--
tg


Top
2017 / 2014 NEC & Related Books and Study Guides
#108121 - 06/02/04 07:33 PM Re: What's Wrong?
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
Well, completely ignoring the "Non Metallic Cable in Free Air" to the right of the Panel, how about flagging the lovely multi colored (other than white, white identified, or bare copper / Aluminum) going to the "neutral" / Grounded buss?
Top
#108122 - 06/02/04 09:06 PM Re: What's Wrong?
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Interesting how some of the NM sheathing is inside the panel, and some is cut way too short.

Quote:
how about flagging the lovely multi colored...


Patriotism. Speaking of flagging, June 14th is Flag Day.

Here's the real punchline:
My wife took this picture. Really!
Top
#108123 - 06/02/04 11:30 PM Re: What's Wrong?
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
Thinkgood... Good to hear your wife is keeping an eye out for forum material But this looks like its in someones basement, a friend of a friend of a friend? ... I wonder if the "thrifty nickel" guys who did an installation I came across moved! Shame for that QO panel to be treated this way!

-Randy
Top
#108124 - 06/03/04 03:24 AM Re: What's Wrong?
pauluk Offline
Member
Registered: 08/11/01
Posts: 7520
Loc: Norfolk, England
Quote:
Shame for that QO panel to be treated this way!

Definitely -- All that lovely wide-open space. (Those who have seen the pics of British panels know what I mean.... )
Top
#108125 - 06/03/04 04:41 PM Re: What's Wrong?
ThinkGood Offline
Member
Registered: 08/07/02
Posts: 1081
Loc: Milwaukee, WI
Quote:
a friend of a friend of a friend?


House hunting!
Top
#108126 - 06/03/04 07:02 PM Re: What's Wrong?
n1ist Offline
Member
Registered: 02/13/02
Posts: 183
Loc: Malden MA
Looks like a work in progress. Seems that someone is adding some new circuits - the hanging yellow romex. There's an open KO in the top of the panel, hopefully for those new ones.

It looks like there are neutrals and grounds mixed on the right bus; I can't see the bonding screw so I am not sure if this is a subpanel or not, but that lone ground coming in thru the conduit on the upper right implies that this is the main. The white reidentified with green as a ground looks a little to small to be restriped green.

Blues are OK for neutral (harmonized wiring uses blue for that) but having blue for both hot and neutral can be confusing.
/mike
Top
#108127 - 06/03/04 07:39 PM Re: What's Wrong?
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
n1ist,

Blue is not OK for use as a neutral. IMO, The blue neutral from the "harmonized" system is a code violation. See article 200.

White cannot be reidentified as green no matter what the size. White may only be reidentified for use as an ungrounded conductor as part of a cable assembly.

Peter
_________________________
Peter
Top
#108128 - 06/04/04 03:51 AM Re: What's Wrong?
Texas_Ranger Offline
Member
Registered: 12/17/01
Posts: 2391
Loc: Vienna, Austria
I also like the way the yellow NM is run to the bottom right breaker. Guess they didn't try to put on the panel cover so far
Top
#108129 - 06/05/04 11:05 PM Re: What's Wrong?
DougW Offline
Member
Registered: 06/08/03
Posts: 1143
Loc: North Chicago, IL
At least it's yellow NM, and not the yellow extension cord seen elsewhere in these pages!
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 01/22/05
Posts: 5316
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (sparkync), 67 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals