#10771 - 06/18/02 07:34 AM sub panel
aldav53 Offline
Member
Registered: 08/22/01
Posts: 545
Loc: Chandler, AZ USA
I'm installing a 60a sub panel on a residential home feeding it with a 60a breaker using #6 thhn, I should be able to use a 100a panel box for it and stay within the code, right?
_________________________
The Golden Rule - "The man with the gold makes the rule"
Top
Work Gear for Electricians and the Trades
#10772 - 06/18/02 05:48 PM Re: sub panel
Bjarney Offline
Moderator
Registered: 04/10/02
Posts: 2527
Loc: West-Southern Inner-Northeast ...
yup.