#107704 - 08/12/04 05:35 AM Is this ground bar OK
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
came across this ground bar in a otherwise normal & clean looking panel... I didn't make a huge issue of it to the owner of the store, but I did note it in the contract.....


2014 / 2011 NEC & Related Books and Study Guides
#107705 - 08/12/04 09:09 AM Re: Is this ground bar OK
cpal Offline

Registered: 05/17/04
Posts: 165
Loc: Cohasset MA
Are those sheetmetal screws w/washers??

looks a little shakey 250.8 maybe 110.3 (B)??

#107706 - 08/12/04 09:27 AM Re: Is this ground bar OK
dougwells Offline


Registered: 05/03/03
Posts: 1226
Loc: kamloops BC Canada
those screws are called Wafer teks they are all in in , I would use them mounting boxes to steel studding.

#107707 - 08/12/04 09:31 AM Re: Is this ground bar OK
CTwireman Offline

Registered: 02/07/02
Posts: 839
Loc: Connecticut, USA
Looks like a GE ground bar in a Cutler Hammer panel. Not quite compatible.


#107708 - 08/12/04 03:01 PM Re: Is this ground bar OK
necbuff Offline

Registered: 07/08/04
Posts: 27
Loc: Lebanon Tn USA
I don't believe this installation is code compliant. Sheet metal screws are not permitted to connect grounding conductors to enclosures. 250.8........... In this case, tek (self tapping) screws.
Kenny Wilee

#107709 - 08/12/04 04:13 PM Re: Is this ground bar OK
e57 Offline

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Is it me, or does that bar look like it was cut in half for some reason?

If so both are a no-go.
Mark Heller
"Well - I oughta....." -Jackie Gleason

#107710 - 08/12/04 05:47 PM Re: Is this ground bar OK
Sir Arcsalot Offline

Registered: 11/17/03
Posts: 117
Loc: Lynden, Washington
Is it me, or does that bar look like it was cut in half for some reason?

Hmmm... split busses are BAD NEWS any way you look at them!!!!!!!

I just could not resist...!
No wire bias here- I'm standing on neutral ground.

#107711 - 08/12/04 10:13 PM Re: Is this ground bar OK
NORCAL Offline

Registered: 09/25/02
Posts: 805
IMO, GE has the worst ground bars around, that split is "normal" for them.

#107712 - 08/13/04 02:43 AM Re: Is this ground bar OK
PCBelarge Offline

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
This poses an interesting situation for inspectors.
Do we violate the installation for not using the proper listed equipment for the enclosure, or do we say at least they separated the equipment grounds from the neutral so I am satisfied?
This is a very typical installation I see almost everyday.
This is clearly a violation of 110.3(B), but...

I will say this; I have seen large faults where the connection of the fittings and the screws were scortched - obviously not a good sign for the fault current path.

Pierre Belarge

#107713 - 08/13/04 12:46 PM Re: Is this ground bar OK
Lostazhell Offline

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
110.3(B) is the first thing that came to mind with me when I saw this also... The thing I mostly was concerned about was that the panel can is being used as the bonding means (No separate EGC coming in with the feeders via EMT). If it comes down to clearing a fault on the 60A 240V A/C circuit which is connected in this panel, will the buttonheads or wafer teks be reliable in doing so?

Could this technically fall under 250.8?