#107439 - 08/26/04 10:53 AM Marina Telephone Flexible Conduit
Admin Offline

Administrator
Member
Registered: 10/07/00
Posts: 3417
Loc: NY, USA
Quote:
The attached photos show telephone cable installed in such a way as to make me forget what I was doing and overlook for a time the supports missing on cables. If anyone recognizes the location, please do not state where it is. I asked permission to post these pictures as long as I did not say where they were taken.

1- The flexible conduits (and cables) need supports within 12" of the cabinets and at 3' intervals thereafter across the deck. NEC 350.30, 356.30

2- The flexible cable connection to the receptacle box is damaged and requires support as above. NEC 350.24

3- I should have checked the telephone cabling inside the hose, it must be listed for a wet location. The raceway (garden hose) is not listed for its use. NEC 800.4, 110.3(B), 800.6

4- The receptacles were GFCI protected by a breaker, but the cover was needing to be weatherproof while-in-use. NEC 406.8 (B)(1)

Shane


Top
2017 / 2014 NEC & Related Books and Study Guides
#107440 - 09/26/04 07:03 PM Re: Marina Telephone Flexible Conduit
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
No, no way... definately no way... Please tell me when the NEC said "Garden hose is a permitted raceway?" (Question not comment.) At least you can do what I know somebody said in another post, "Saving materials by combining water and electrical service." I'd like to see that hose connected to a faucet...
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#107441 - 01/01/07 07:21 PM Re: Marina Telephone Flexible Conduit
ShockMe77 Offline
Member
Registered: 06/11/05
Posts: 821
Loc: Rahway, New Jersey
BUMP!

From time to time I look at some of these old threads to further familiarize myself with code articles and violations. This one I thought was pretty comical. Does the flex coming from out of the enclosure to the weatherproof box violate bending radius requirements?
Top
#107442 - 01/02/07 08:35 AM Re: Marina Telephone Flexible Conduit
n1ist Offline
Member
Registered: 02/13/02
Posts: 183
Loc: Malden MA
The top garden hose certainly looks like it does...
Top
#107443 - 01/02/07 12:35 PM Re: Marina Telephone Flexible Conduit
Zapped Offline
Member
Registered: 10/01/02
Posts: 482
Loc: Huntington Beach, CA, USA
I think ShockMe77 and I are seeing the same thing. Isn't that a couple of garden hoses (bottom left and top)?

Is this a bad use of garden hoses for data/com or a bad use of a single-ganged outdoor box for a water junction? Either way, I don't like it!
Top
#107444 - 01/02/07 12:43 PM Re: Marina Telephone Flexible Conduit
EV607797 Offline
Member
Registered: 10/25/06
Posts: 744
Loc: Fredericksburg, VA, USA
I see shoddy workmanship at marinas all the time. PVC sagging or pulling apart is probably the most common. White PVC couplings and elbows with gray PVC for electrical work is probably next. They get pretty creative with garden hoses too, but that's probably one of the better botch jobs that I have seen.
_________________________
---Ed---

"But the guy at Home Depot said it would work."
Top
#107445 - 01/02/07 09:05 PM Re: Marina Telephone Flexible Conduit
Lostazhell Offline
Member
Registered: 02/21/04
Posts: 1428
Loc: Bakersfield, CA (Originally Or...
That would never fly here! The connector isn't listed for a garden hose!
Top
#107446 - 01/03/07 04:45 PM Re: Marina Telephone Flexible Conduit
Theelectrikid Offline
Member
Registered: 04/30/04
Posts: 810
Loc: Levittown, PA
Quote:
That would never fly here! The connector isn't listed for a garden hose!


That's the least of their problems...

Ian (Calling ****** Construction to demo a singlewide!) A.
_________________________
Is there anyone on board who knows how to fly a plane?
Top
#107447 - 01/05/07 02:36 AM Re: Marina Telephone Flexible Conduit
iwire Offline
Moderator
Registered: 01/05/03
Posts: 4391
Loc: North Attleboro, MA USA
I have to ask.

What NEC code violation code be cited?

Lets leave 'Neat and Workmanlike' out of it.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts
Top
#107448 - 01/05/07 09:43 AM Re: Marina Telephone Flexible Conduit
RSmike Offline
Member
Registered: 11/27/02
Posts: 134
Loc: Holland, MI USA
I can't believe I'm about to argue in favor of parts of this.....

If the phone cable inside the garden hose is rated for direct exposure to sunlight, saltwater, fishhooks, etc. does inserting it into garden hose violate anything?

If done neatly what violations exist.

And please list code sections.

RSlater,
RSmike
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 07/05/02
Posts: 8211
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 45 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals