The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Topic Options
Rate This Topic
#107436 - 09/18/04 05:28 AM DIY Man strikes again!
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
I was called to a house in town here a few months back, to check out some problems that a homeowner had in the house that she and her husband had recently purchased.
One of the problems that had caused the call was, the range-hood had fallen off the wall and shattered the ceramic-top stove.
Closer inspection found that the range was nailed to the wall into timber so thin, you wouldn't even make a picture frame out of it.
But, anyhow, she told me that the rangehood would only work when the stove was turned off, this sounded strange!.
I then turned off the Main switch and took what was left of the rangehood off the wall.
Feeding it, was the thinnest piece of 2-core wire I've ever seen and further inspection found that it was fed from the Stove switch (a 32A circuit).
While I was running a proper circuit back to the switchboard, I noticed this in the roof space:



There's 230V on them red wires.
Then she showed me the Bathroom, the guy that owned the house before-hand, had installed his own heated towel rail, it was rough, as you can see:



But then I turned around, there was anther one behind me, it was slightly worse, it was fed from a light switch, literally!:



Down to this, using white phone wire!:



I'm glad it's all fixed up now, they had young kids too!.
Apparently the previous owner thought himself a bit of a Jack of All Trades.
The visit from the Inspector may have woke him up. GRRR!

{Note to Scott/Bill, feel free to abridge/edit this post if necessary, for loading speed, etc}

{Especially the pictures!!, how did that happen?}

[This message has been edited by Trumpy (edited 09-18-2004).]
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
2014 / 2011 NEC & Related Books and Study Guides
#107437 - 09/26/04 07:42 AM Re: DIY Man strikes again!
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
Just a small footnote.
We (the Fire Brigade) attended a small fire at the guy's new place, which could have burn't the whole house down, had it gone un-discovered.
Caused by a bad cable joint under the floor.
I guess some people never learn, eh!.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#107438 - 09/26/04 12:08 PM Re: DIY Man strikes again!
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
Other side of the world, yet such a familiar look to those pictures.

Top



ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals