#107023 - 12/27/04 05:46 PM Cable Guys and the NEC  
Admin  Offline

Administrator
Member
Joined: Oct 2000
Posts: 3,437
NY, USA
Quote
These photos are of a cable TV install in an apartment complex. The careful eye will note that the support strap is about to pop out, the coupling screws are not tightened down, and there is no connector where the 2" EMT enters the box.

More reasons why I laugh when other trades claim that they follow the NEC.

- John Steinke
[Linked Image]

[Linked Image]


2017 / 2014 NEC & Related Books and Study Guides

#107024 - 12/27/04 06:26 PM Re: Cable Guys and the NEC  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
What section of Article 820 is violated? [Linked Image]


Charlie Eldridge, Indianapolis Utility Power Guy

#107025 - 12/27/04 10:22 PM Re: Cable Guys and the NEC  
e57  Offline
Member
Joined: May 2003
Posts: 2,876
S.F.,CA USA
It seems very "catch all", but I'd say 820.3C "Installation and Use. Section 110.3 shall apply."

"110.3B Installation and Use. Listed or labeled equipment shall be installed and used in accordance with any instructions included in the listing or labeling."

They entered chapter 3 with the use of EMT, and related fittings with thier listings and uses.

And if there is VoIP +/or cable powered telephones in use on the CATV lines, it falls into 800.48 "Where communications wire and cables are installed in a raceway, the raceway shall be either of a type permitted in Chapter 3 and installed in accordance with Chapter 3 or a listed nonmetallic raceway complying with 800.51(J), (K), or (L), as applicable, and installed in accordance with 362.24 through 362.56, where the requirements applicable to electrical nonmetallic tubing apply."

Our inspectors would just mumble "Chapter 3" and walk off. They cut a little less slack for the cabling guys every time they show up to see things like this.


Mark Heller
"Well - I oughta....." -Jackie Gleason

#107026 - 12/27/04 10:26 PM Re: Cable Guys and the NEC  
John Steinke  Offline
Member
Joined: Apr 2001
Posts: 518
Reno,Nv., USA
I believe that Charlie was making the point that "other trades" seem to only concern themselves with that specific part of the code that focuses on their craft.


#107027 - 12/27/04 10:59 PM Re: Cable Guys and the NEC  
CharlieE  Offline
Member
Joined: Apr 2004
Posts: 200
Indianapolis
Thanks John. [Linked Image]

- - - - - - - - - - - - - - - - - - - - - - - - - - -
Charlie Eldridge, Indianapolis, Utility Power Guy


Charlie Eldridge, Indianapolis Utility Power Guy


Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.013s Queries: 14 (0.003s) Memory: 0.7675 MB (Peak: 0.9049 MB) Zlib enabled. Server Time: 2017-03-27 18:27:01 UTC