#106303 - 05/02/05 07:01 PM Prove What's Wrong Here
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
This pic goes into the category of things you just know are wrong....but where is code violated?

What you see is a duplex receptacle mounted in a 3-0 box. It is attached where the box cover usually attaches. There are covers made for this box that hold a single receptacle, but not a duplex. An oversize receptacle coverplate will just about cover the front of the box.

- renosteinke



Top
2014 / 2011 NEC & Related Books and Study Guides
#106304 - 05/02/05 09:23 PM Re: Prove What's Wrong Here
sierra electrician Offline
Member

Registered: 02/12/05
Posts: 220
Loc: North Fork, CA USA
I just took a duplex just like that out of service today and it had a Raco Dup cover made of stamped steel.

Rob

Top
#106305 - 05/02/05 09:38 PM Re: Prove What's Wrong Here
Scott35 Offline

Broom Pusher and
Member

Registered: 10/19/00
Posts: 2724
Loc: Anaheim, CA. USA
I may have 1 or 2 scenarios to ponder as violations:



    [*] Is this Outlet Grounded (Box and Receptacle) - via an EGC?


    [*] Is there adequate free Conductor length in this Box?


And the most obvious: Why no cover? (hee hee ...)

Scott35
_________________________
Scott " 35 " Thompson
Just Say NO To Green Eggs And Ham!

Top
#106306 - 05/02/05 09:54 PM Re: Prove What's Wrong Here
frenchelectrican Offline

Member

Registered: 02/06/03
Posts: 938
Loc: Wi/ Paris France { France for ...
John :


i did see cover for 3-0 and 4-0 verison have duplex verison but i dont like it not much becasue the older cover only have single screw to hold the repectaile in place the later cover have two screw or three screw to really lock the repetcale in place i know Raco do make it


Merci , Marc
_________________________
Pas de problme,il marche n'est-ce pas?"(No problem, it works doesn't it?)


Top
#106307 - 05/03/05 06:56 AM Re: Prove What's Wrong Here
renosteinke Offline
Cat Servant
Member

Registered: 01/22/05
Posts: 5305
Loc: Blue Collar Country
You learn something new every day....

I've never seen the duplex cover for the smaller (3-0) box...didn't know there was one. Maybe this is OK after all?

Sierra- sharp eye! You are correct, the old romex has no ground wire.
As for "free conductor" length, that I'm not so sure about; back then there was no such requirement. Conductors often had insulation skinned off them as they passed through the box, and a very short pigtail twisted and soldered in place, then wrapped with tape.

Top
#106308 - 05/03/05 01:24 PM Re: Prove What's Wrong Here
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Box should be a device box so that the device can be properly installed.
_________________________
Joe Tedesco, NEC Consultant

Top
#106309 - 05/03/05 03:02 PM Re: Prove What's Wrong Here
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
Joe,
The manufacturers make covers for duplex recptacles in octgon boxes, so why would this be an improper installation? (assuming that the cover was actually installed)
Don
_________________________
Don(resqcapt19)

Top
#106310 - 05/03/05 03:23 PM Re: Prove What's Wrong Here
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Don:

I am aware of that cover, and I am commenting on this "incorrect" installation.

The receptacle on the round cover is secured to the octagon box using the two 8/32 screws that are used to secure the entire assembly.

The installation here is not correct under any circumstances!
_________________________
Joe Tedesco, NEC Consultant

Top
#106311 - 05/03/05 03:37 PM Re: Prove What's Wrong Here
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I've seen many of these that have the mounting ears/yoke cut off right at the recptacle. The receptacle is held to the cover with the single 6-32 in the center of the cover, while the cover itself is screwed to the box with the usual 8-32s.

Top
#106312 - 05/03/05 04:03 PM Re: Prove What's Wrong Here
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA


Here is that cover --- and the proper receptacle is made without a yoke (strap) and the single 6/32 screw is actually a violation since this would be a "cover mounted" receptacle.
_________________________
Joe Tedesco, NEC Consultant

Top