#106279 - 05/02/05 07:14 PM DIY HVAC- an easy violation
Webmaster Offline

Administrator
Member

Registered: 10/07/00
Posts: 3142
Loc: NY, USA
 Quote:
This gas furnace has a circulating fan at the top. Someone decided to power it by running a piecs of 'zip cord'.
- Wires are required to be in a raceway (300.3B). Romex, incidently, is a 'raceway.' You might consider 'zip cord' a cable, but-
- You aren't allowed to use zip cord in place of a permanent wiring method (402.11).
- All splices must be in a box (appliance cases are often considered a 'box')(300.15).

In addition, the 'zip cord' might be smaller than #14 (210.19A4); We can safely assume that this is not a dedicated circuit (422.12); and, While the unit MAY pre-date a grounding requirement. that wouldn't be a bad idea!

- renosteinke



Top
2014 / 2011 NEC & Related Books and Study Guides
#106280 - 05/04/05 04:59 PM Re: DIY HVAC- an easy violation
Trumpy Offline

Member

Registered: 07/05/02
Posts: 8540
Loc: SI,New Zealand
John,
 Quote:
You might consider 'zip cord' a cable

Not in my book it isn't.
Cable in my interpretation of the word, means, individual wires (stranded or solid) insulated with an appropriately rated insulation.
These two insulated conductors are then covered with an outer sheathing of equal voltage rating to the core insulation.
This sort of cable is called Double Insulated over here.
Using Single insulated wire as fixed wiring over here will get you into a LOT of trouble.
_________________________
Let's face it, these days if you're not young, you're old - Red Green grin

Top
#106281 - 05/06/05 10:50 AM Re: DIY HVAC- an easy violation
mxslick Offline
Member

Registered: 10/24/04
Posts: 785
Loc: Atomic City, ID USA
Taking a look at the soot pattern in the area of the zip cord, as well as the flying splice and the exposed metal of the stack, makes me wonder if the previous cord burned?

The wall looks to be perfectly clean on the other side....
_________________________
Stupid should be painful.