#105366 - 11/20/04 04:45 AM How many violations can you find?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA




Courtesy: www.nachi.org
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#105367 - 11/20/04 08:07 AM Re: How many violations can you find?
NORCAL Offline
Member

Registered: 09/25/02
Posts: 807
Is it a split buss panel? It appears to be one but my monitor leaves much to be desired,if it is it would explain the main lug kit instead of a breaker,but I count 5 mains. Some of the most obvious violations are: double lugged conductor and unprotected also.The SE cable below the main lugs, I assume is supplying another panel?

The "workmanship" and the "quality" of the panel go well together : Very poor,the damage at least will mean that it has to go.

PS 384-16 (a) all the way back to the 1965 NEC says no more than 2 mains in a panelboard, the change occured in that edition,but there was some tweaking of the exceptions over the years since.

Top
#105368 - 11/20/04 08:23 AM Re: How many violations can you find?
Sir Arcsalot Offline
Member

Registered: 11/17/03
Posts: 117
Loc: Lynden, Washington
Are those ZZZZZINSMOKE breakers? If so, not a technical violation but a serious potential hazard nonetheless.

Just my opinion.
_________________________
No wire bias here- I'm standing on neutral ground.

Top
#105369 - 11/20/04 09:27 AM Re: How many violations can you find?
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
It is I believe a split-bus panel used as service equipment. The 5 mains is not a violation but the taps to the main lugs are and may have contributed to their demise. Looks like some conductors enter through KO's without connectors too.
_________________________
John

Top
#105370 - 11/20/04 09:46 AM Re: How many violations can you find?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
What about the egg's, would twisting them altogether be ok and all set into one lug?
_________________________
Joe Tedesco, NEC Consultant

Top
#105371 - 11/20/04 03:30 PM Re: How many violations can you find?
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Nice weldage...

Top