#105316 - 09/06/04 04:43 AM See anything wrong here?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#105317 - 09/06/04 05:04 AM Re: See anything wrong here?
Megawatt Offline
Member

Registered: 03/11/04
Posts: 74
Loc: Lexington,Ky, USA
Where do You start ?? Must not own any side cutters !
Around here, I would install a Disc, & run flex to the Waterheater. Makes a nice looking installation.
Is the romex #10 ??

Top
#105318 - 09/06/04 06:35 AM Re: See anything wrong here?
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
How could anyone walk away from this?
_________________________
John

Top
#105319 - 09/06/04 06:44 AM Re: See anything wrong here?
capt al Offline
Member

Registered: 06/20/04
Posts: 203
Loc: Norton, Ma USA
Always nice to leave the covers off of the elements. No one would ever put their hand near there.

Top
#105320 - 09/06/04 07:07 AM Re: See anything wrong here?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Do we know this is complete?

The breaker can be the disconnect.

It is tough to give answers without knowing the details.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#105321 - 09/06/04 07:12 AM Re: See anything wrong here?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Bob:

This work was what the AHJ found during the Final.

Your opinion of what you see wrong here will be appreciated.
_________________________
Joe Tedesco, NEC Consultant

Top
#105322 - 09/06/04 08:38 AM Re: See anything wrong here?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Well if this is what it looked for the final the inspector should fail it.

The only reason I can say for sure would be lack of support of the NM 334.30 and the open cover that Capt. Al mentioned 110.27(A).

The other issues, correct wire temp rating and lack of disconnect can not be commented on from this picture alone.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#105323 - 09/06/04 08:44 AM Re: See anything wrong here?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Bob: Discussion!

That's healthy, and that is what we do here!

I make comments all of the time to help people understand the subject of the installation.

Pictures are always helpful, but cannot show every single item.
_________________________
Joe Tedesco, NEC Consultant

Top
#105324 - 09/06/04 08:46 AM Re: See anything wrong here?
DougW Offline
Member

Registered: 06/08/03
Posts: 1083
Loc: North Chicago, IL
Without knowing the conductr size, here's a quick take...

Failure to secure NM cable within appropriate distance... (336-18 '96 NEC)

Failure to secure/support NM cable @ required intervals along run...(336-18 '96 NEC)

Failure to protect NM cable from physical damage... (336-6(b) '96 NEC)

Unprotected access to equipment (failure to install in an approved manner)... (422-6 '96 NEC)

Top
#105325 - 09/06/04 08:57 AM Re: See anything wrong here?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
Doug you are Chicago sparky right? As such you may not be used to seeing NM but it is often run exposed.

In my opinion if it was supported properly without the loop to the floor, physical damage would not be an issue at least here in MA and RI.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top