#105311 - 09/06/04 07:02 AM Inspection request here, please discuss!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Inspection request here, please discuss!

[Linked Image]


Joe Tedesco, NEC Consultant

2017 / 2014 NEC & Related Books and Study Guides

#105312 - 09/06/04 11:53 AM Re: Inspection request here, please discuss!  
DougW  Offline
Member
Joined: Jun 2003
Posts: 1,143
North Chicago, IL
What's with the coiled cable behind the tank?

What's in the j-box on the wall behind the tank?

What's the raceway for that's next to the j-box?

Do those runs of flex have an equipment grounding conductor installed and properly terminated?


#105313 - 09/06/04 09:29 PM Re: Inspection request here, please discuss!  
harold endean  Offline
Member
Joined: Feb 2002
Posts: 2,233
Boonton, NJ
I see no disconnect for the well pump. Or even a lockable disconnect, plus that looks like a water heater next to the well. Same goes for that. You would need a disconnect for the water heater and depending on which code you are using, a locakable disconnect might be acceptable. What about bonding jumpers across the hot and cold pipes? Is there a cover for that big j-box? How about straps on the EMT pipe. Did Doug or I get what you were looking for?


#105314 - 09/06/04 09:34 PM Re: Inspection request here, please discuss!  
Joe Tedesco  Offline
Member
Joined: Oct 2000
Posts: 2,749
Boston, Massachusetts USA
Yes, and you answered the question.


Joe Tedesco, NEC Consultant

#105315 - 09/08/04 07:51 PM Re: Inspection request here, please discuss!  
velect  Offline
Member
Joined: May 2004
Posts: 81
st joseph mi usa
Maybe the distribution panel is in sight



Member Spotlight
Attic Rat
Attic Rat
Bergen Co.,N.J. USA
Posts: 524
Joined: December 2003
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.016s Queries: 14 (0.003s) Memory: 0.7650 MB (Peak: 0.9044 MB) Zlib enabled. Server Time: 2017-03-25 04:00:55 UTC