#105255 - 07/30/04 04:13 PM Mixing Line Voltage and Thermostat Wires in aAC Disconnect
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Mixing Line Voltage and Thermostat Wires in a AC Disconnect Switch.

What's the consensus? Seems to be a violation of the code?

_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#105256 - 08/01/04 05:32 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
velect Offline
Member

Registered: 05/01/04
Posts: 79
Loc: st joseph mi usa
Where is the ground wire to the unit

I hate it when guys ramset boxes to a wall

Top
#105257 - 08/01/04 05:37 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
It was not installed!

and ... Posted: Jul 31, 2004 8:43 AM Post subject: OK!

--------------------------------------------------------------------------------

Dennis: OK, I think you done real good! and below see also the discussion on the question first posted in the link above:




The low voltage thermostat wires are not permitted to be run in the same cable or conduit because they do not have sufficient construction specifications to permit them to be installed with electric light, power conductors and any failure of the cable insulation due to a fault could lead to hazardous voltages being imposed on the thermostat circuit conductors.

The use of the same insulation for circuits up to 600 volts for both AC and DC is acceptable when run in the same cable or conduit, but not for this application.

It is better to see that thermostat wiring run in a separate cable or conduit, or wrapped around the cable or conduit that will supply the unit.
_________________________
Joe Tedesco, NEC Consultant

Top
#105258 - 08/01/04 07:12 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
SteveMc Offline
Member

Registered: 02/05/04
Posts: 61
Loc: Rock Hill, SC
Agreed it's not a good practice, but if the wiring is all 600v rated, is it a violation? What Code reference, so I can tell the HVAC guys next time I see this done.

Top
#105259 - 08/01/04 07:29 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
 Quote:
300.3(C) Conductors of Different Systems.

(1) 600 Volts, Nominal, or Less.

Conductors of circuits rated 600 volts, nominal, or less, ac circuits, and dc circuits shall be permitted to occupy the same equipment wiring enclosure, cable, or raceway.

All conductors shall have an insulation rating equal to at least the maximum circuit voltage applied to any conductor within the enclosure, cable, or raceway.

Exception: For solar photovoltaic systems in accordance with 690.4(B).

FPN:See 725.55(A) for Class 2 and Class 3 circuit conductors.
_________________________
Joe Tedesco, NEC Consultant

Top
#105260 - 08/01/04 08:14 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
725.55 does not permit under any circumstance for Class 2 conductors to be installed in RACEWAYS with any power conductors, even associated conductors are not permitted in the same raceway.
Enclosures and other items yes, under specific restrictions, but not raceways.

Pierre
_________________________
Pierre Belarge

Top
#105261 - 08/01/04 08:46 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
Lostazhell Offline
Member

Registered: 02/21/04
Posts: 1248
Loc: Bakersfield, CA (Originally Or...
where is the T-stat wire gaining access to the electrical system here anyways??? It looks like its spliced into the #12TW's on the left? This is a strange installation from what I'm used to...

-Randy

Top
#105262 - 08/02/04 01:09 AM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
Big Jim Offline
Member

Registered: 07/18/03
Posts: 377
Loc: Denver, CO USA
OK, the picture is not too clear to me. We have the heavy black and light blue conductor pairs that look like line and load. We have an orange and a blue spliced to the aux contacts on the breaker. And we have some sort of a coil of unidentified white wire that doesn't really seem to start or end anywhere. What's with the white - what is it? Where does it originate and terminate?

Top
#105263 - 08/12/04 05:11 PM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
skingusmc Offline
Member

Registered: 05/27/04
Posts: 116
Loc: Simi Valley, CA USA
The blue wire on the very left of the photo comin gout of the yellow wire nut goes up and then back down ans seems to end in a spade connector that is not attached to anything. The smaller blue wire from the same yellow worenut goes almost directly to the right and ends up in the coil of white, green, red, and yellow wire. What is going on here?
_________________________
Thanks
Steve

Top
#105264 - 08/16/04 02:40 PM Re: Mixing Line Voltage and Thermostat Wires in aAC Disconnect
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
No you can not run class 1 and 2 in the same raceway but you can reclassify class 2 or 3 circuits to class 1 then run them in the same conduit with other class 1 conductors 725.52(A)Exception No. 2

I doubt highly that is the case of the wiring in Joe's Picture.

Bob
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top