#105207 - 07/12/04 03:03 PM Was this encasement really necessary?
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Was this encasement really necessary?

_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#105208 - 07/12/04 03:16 PM Re: Was this encasement really necessary?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
IMO overkill for this short distance, but given the wording of the NEC I believe the inspector can require this.

I have done this to get about 40' to 60' inside of buildings.

Bob

FWIW I hope there are some dowels into the foundation to carry the weight of this.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#105209 - 07/12/04 05:24 PM Re: Was this encasement really necessary?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
Does this make it "outside the building"?

Top
#105210 - 07/12/04 05:56 PM Re: Was this encasement really necessary?
electricman2 Offline
Member

Registered: 11/09/03
Posts: 234
Loc: Thomasville, NC USA
Looks like it meets 230.6(2)from here. Cant tell if it is 2" all the way around though.
_________________________
John

Top
#105211 - 07/12/04 07:34 PM Re: Was this encasement really necessary?
PCBelarge Offline
Member

Registered: 06/08/03
Posts: 657
Loc: Dobbs Ferry, NY, USA
Picture a 15 inch soffit overhang for the roof of a house. Now picture the RMC raceway for a mast run up the side of the house and throught the soffit and in the void up through the roof. There was about 15 inches of RMC in the space. The inspector made the contractor incase that portion in 2 inches of concrete, as he said it was inside the house....HMMMM

Pierre
_________________________
Pierre Belarge

Top
#105212 - 07/12/04 08:40 PM Re: Was this encasement really necessary?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
Now picture this... A guy shows up to do demo for a remodel. Sees a 6"X6" concrete column (somewhere outside of this panel room) and thinks to himself... Well it's non-structural, what's it for... Jackhammer, or Diamond saw? Boom!

If it were just the conduit, they would call an Electrician, right?

Just so happens, I had to call the Inspector for 230.70A today, we get a different answer everytime! Today, they said they'll get back to me... I have a job where we'll need to go 38' into the building.
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#105213 - 07/13/04 03:16 PM Re: Was this encasement really necessary?
Electricmanscott Offline
Member

Registered: 01/12/02
Posts: 1478
Loc: Holden, MA USA
The picture also seems to me to be overkill. Is this the only portion in the building? Is the other side of that wall outdoors or another part of the building that the pipe goes through?
E57 I don't see how there could even be a question for 38' inside the building.

Top
#105214 - 07/13/04 11:35 PM Re: Was this encasement really necessary?
e57 Offline
Member

Registered: 05/27/03
Posts: 2837
Loc: S.F.,CA USA
No other place to enter building, no other place for service, 38' to get there... (22' back 16' down, all service drops)

Cusomer is building the Taj Mahal, no kidding turrets and onion domes. Boss wants exposed, customer is taking a hissy fit about a 2" pipe running all over his palace. We'll let the inspector make the call...

230.70A is left pretty much up to the inspector.

Personal thought its that it needs to be clarified!

In the past they've OK'ed it! Sometimes they don't... I'm still pushing for under-ground from the pole. But PG&E takes about 18 months to connect! The Inspector hasn't called me back yet. Let you know what he says...

[This message has been edited by e57 (edited 07-14-2004).]
_________________________
Mark Heller
"Well - I oughta....." -Jackie Gleason

Top
#105215 - 07/14/04 01:51 AM Re: Was this encasement really necessary?
iwire Offline
Moderator

Registered: 01/05/03
Posts: 4343
Loc: North Attleboro, MA USA
E, I can not imagine going 38' into the building without encasement. There is no chance that would be allowed here.

As far as demo guys cutting into it that can always be a problem.

I had to help repair a 4" conduit that was cut by a concrete saw, it was one of eight sets of 600 kcmils that feed a 3000 amp 480 switch gear.

The operator of the saw was OK but it knocked out a neighborhood.
_________________________
Bob Badger
Construction & Maintenance Electrician
Massachusetts

Top
#105216 - 07/14/04 08:41 AM Re: Was this encasement really necessary?
SolarPowered Offline
Member

Registered: 07/05/04
Posts: 615
Loc: Palo Alto, CA, USA
Dumb question from someone not privy to the sausage-making, err, code-making process: What's the point of the encasement? I can't see how RMC by itself would be measurably less safe than RMC encased in concrete. In theory, sure, anything in 2" of concrete is more protected than the same thing without the concrete. But, in practice, RMC is practically indestructible, absent a structural collapse or vehicle impact.