#104649 - 09/24/03 11:41 AM Other Equipment in This Junction Box
Joe Tedesco Offline

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
Is this allowed?

Joe Tedesco, NEC Consultant

2014 / 2011 NEC & Related Books and Study Guides
#104650 - 09/24/03 04:33 PM Re: Other Equipment in This Junction Box
Gus1999 Offline

Registered: 12/11/02
Posts: 25
Loc: Los Angeles, CA, USA
I looks like some form of LV wiring is sharing those conduits. This alone is not allowed!

#104651 - 09/26/03 03:59 AM Re: Other Equipment in This Junction Box
electure Offline


Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
The 2x4 certainly doesn't belong in there.
It looks like the cover on the "LR" conduit body couldn't be removed.
Unused openings in box aren't sealed.
Sorry, Gus, but I must disagree with you. All the conductors appear to be THWN, 600V rated, and may occupy the same raceways or enclosures (see 300.3(C)(1))...S