#104619 - 09/10/03 02:10 PM How Low Can You Go!!
Joe Tedesco Offline
Member

Registered: 10/07/00
Posts: 3325
Loc: Boston, Massachusetts USA
This is a service entrance conductor Drip Loop and has limitations according to the NEC.

What is the minimum distance to the "loop"?

_________________________
Joe Tedesco, NEC Consultant

Top
2014 / 2011 NEC & Related Books and Study Guides
#104620 - 09/10/03 02:49 PM Re: How Low Can You Go!!
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
At a quick code clook-up, I would think this is covered by 230.24(B).

Is there a messenger wire there? I can't see one, so I'm guessing that (1) wouldn't apply, and this drop would be covered by either (2) requiring a 12 ft. clearance or (4) requiring 18 ft. if there's truck traffic.

Have I missed anything?

Top
#104621 - 09/10/03 03:45 PM Re: How Low Can You Go!!
pauluk Offline
Member

Registered: 08/11/01
Posts: 7693
Loc: Norfolk, England
OK, I think I misread that first time. Part (1) applies to the loop so the minimum is 10 ft.

How high is this loop? From an upstretched arm, I'd guess around 8 ft. ?