Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA


Is the color GREEN OK for use to identify the Grounding Electrode Conductor, or is it a violation to use it to identify a GEC?

Your Vote Here Please!

USE THE NEC ONLY PLEASE!

[This message has been edited by Joe Tedesco (edited 03-07-2003).]
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#104502 - 03/07/03 12:08 PM Re: Vote for the GEC Color Here!!
resqcapt19 Offline
Member
Registered: 11/10/00
Posts: 2148
Loc: IL
310.12(C) requires the grounding electrode conductor to be green.
Don
_________________________
Don(resqcapt19)
Top
#104503 - 03/07/03 12:45 PM Re: Vote for the GEC Color Here!!
cubby964 Offline
Member
Registered: 10/18/02
Posts: 67
Loc: USA
I am securely on the fence as to any requirements, but I vote Green.
Rationale: none other than the fact that green indicates groundING everywhere else in the Code. (And yes, because we've always done it that way).
I also vote for a change to the Code. (if I can do that here)
Top
#104504 - 03/07/03 01:44 PM Re: Vote for the GEC Color Here!!
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
Green is allowed to identiy the equipment grounding conductor. This is a grounding electrode conductor which is defined as the conductor that connects the grounding electrode to the equipment grounding conductor, the grounded conductor or both. My vote is absolutely not.
Top
#104505 - 03/07/03 01:54 PM Re: Vote for the GEC Color Here!!
Electra Offline
Member
Registered: 07/29/02
Posts: 38
Loc: Portland, Oregon, USA
Isn't that conduit also supposed to be bonded to the GEC?

Here in Portland, I have only seen the GEC as green.
Top
#104506 - 03/07/03 02:30 PM Re: Vote for the GEC Color Here!!
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
I could see some diagnostic instances where a EGC should not be confused with a GEC, therefore some means of differentiating would be prudent.

OTOH, the NEC would seem moot on the subject, as if it is not a safety issue
Top
#104507 - 03/07/03 04:22 PM Re: Vote for the GEC Color Here!!
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
Hi Joe,

How about........ (key word 'grounding')

2002 NEC:
Article 100 Definitions:

Quote:
Grounded. Connected to earth or to some conducting body that serves in place of the earth.


Quote:
Grounded Conductor. A system or circuit conductor that is intentionally grounded.


Quote:
Grounding Conductor. A conductor used to connect equipment or the grounded circuit of a wiring system to a grounding electrode or electrodes.

The later mixes the words "grounding" and "grounded" in a single definition that actually referes to two separate terms used elsewhere in the NEC.

What a conundrum!(a : a question or problem having only a conjectural answer b : an intricate and difficult problem)

Since there is no clear answer to be found in the NEC, but the words "grounding conductor" are used in reference to (A) the "grounding electrode conductor", which never specifies an identification in reference to color, and (B) the " equipment grounding conductor" which specifies an identification in reference to color (green),we are left to wonder what color if any, we are to use.
It would seem logical based on the above definitions to choose green since one is specified and one is not.

Hummm........

Dave
_________________________
Dave
Top
#104508 - 03/07/03 04:45 PM Re: Vote for the GEC Color Here!!
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
Quote:
Since there is no clear answer to be found in the NEC


shall we move on to bonding idenification?
Top
#104509 - 03/07/03 05:37 PM Re: Vote for the GEC Color Here!!
WebSparky Offline
Member
Registered: 02/21/03
Posts: 138
Loc: Cleveland, Ohio
Hey sparky!

What did ya have in-mind?
_________________________
Dave
Top
#104510 - 03/07/03 05:45 PM Re: Vote for the GEC Color Here!!
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
WebSparky.
there is much controversy over 'bonding' vs. GEC's or EGC's , so would identification follow suit??

~S
Top
Page 1 of 2 1 2 >

Member Spotlight
Member Since: 04/03/02
Posts: 6776
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (gfretwell), 48 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals