The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Calling all Non-US members!! (Non-US only)
by aussie240
Today at 02:39 AM
Photo Upload Tutorial
by DanK
Yesterday at 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
New in the Gallery:
12.5A through 0.75mm flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 9
Texas_Ranger 8
sparkyinak 7
Trumpy 6
Who's Online
0 registered (), 109 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Page 1 of 2 1 2 >
Topic Options
Rate This Topic
#10334 - 06/06/02 02:05 PM What changed, the wire or the breaker?
master66 Offline
Member

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
Question;
According to the 2002 NEC, what size copper conductors are required for a 3-Phase 120/240V Delta 400 Amp, 600 Amp and 800 Amp service? Figure 1 set of 4 conductors per conduit (PVC).
The answer may surprise you. It surprised me (if I read the code correctly).

Top
Work Gear for Electricians and the Trades

Work Gear for Electricians and the Trades
Work Gear for Electricians and the Trades
Arc Flash Clothing, Gloves, KneePads, Tool Belts, Pouches, Tool Carriers, etc. etc....

#10335 - 06/06/02 07:10 PM Re: What changed, the wire or the breaker?
electure Offline

Member

Registered: 12/24/00
Posts: 4226
Loc: Fullerton, CA USA
I think I'd parallel some 4/0 or 250 in each of the apps (do your own math!).

Top
#10336 - 06/07/02 07:39 AM Re: What changed, the wire or the breaker?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
How many service OCPDs are there and what is the calculated load on the services? It does make a difference in the code answer to this question.
Don(resqcapt19)
_________________________
Don(resqcapt19)

Top
#10337 - 06/08/02 06:23 PM Re: What changed, the wire or the breaker?
master66 Offline
Member

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
resqcapt19,

Thanks for the reply.

There is one OCPD and assume the calculated load is the same (or slightly under) the OCPD rating.

Top
#10338 - 06/08/02 07:47 PM Re: What changed, the wire or the breaker?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
master66,
I don't see any changes here. Any conductor or set of conductors with an ampacity exceeding 350 amps can be used with the 400 amp service, over 500 amps for the 600 amp service and over 700 amps for the 800 amp serivce is permitted by Exception #2 to 230.90(A).
Don

[This message has been edited by resqcapt19 (edited 06-09-2002).]
_________________________
Don(resqcapt19)

Top
#10339 - 06/09/02 06:36 PM Re: What changed, the wire or the breaker?
master66 Offline
Member

Registered: 04/18/02
Posts: 260
Loc: Masontown, PA, USA
resqcapt19,

This is how I have done it for years but was told recently that the SE conductor could not be rated less that the OCPD and that the rating had to be calculated in accordance with 310.15. In my case, for a machine shop, I believe that the neutral should be counted.

I have also asked other inspectors this same question and was told the same as you said.

Who's right?

Top
#10340 - 06/09/02 07:25 PM Re: What changed, the wire or the breaker?
resqcapt19 Offline
Member

Registered: 11/10/00
Posts: 2209
Loc: IL
master66
If derating is required because of more then 3 current carrying conductors or high ambient temperature, this changes the ampacity of the conductors. The ampacity after derating must be equal or greater then the numbers in my earlier post. This in not new. Table 310-16 ampacities are only for 3 or less conductors and an ambient of 30°C. If your grounded conductor is in fact a current carrying conductor, then you would have to use conductors with a table ampacity of 438 amps for a 400 amp service. This would require 600 kcmil or parallel 3/0s in seperate conduits, or parallel 4/0s in a common raceway. The wire sizes I have listed assume a 90°C insutlation.
Don
_________________________
Don(resqcapt19)

Top
#10341 - 06/09/02 07:38 PM Re: What changed, the wire or the breaker?
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
If the calculated load of your 400 amp service is 380 amps or less then 500 MCM copper is fine but if your load is 381 amps then you would need to use 600 MCM. The same goes for the 600 amp and 800 amp services. As long as the calculated load does not exceed the conductors rating your ok. What do you mean by "I believe the neutral should be counted"? If you are saying that the neutral should be counted for derating purposes I am not sure why. If this is a delta service the neutral is only carrying the unbalanced load of a single phase winding on the transformer so harmonics should not be a problem.
_________________________
Curt Swartz

Top
#10342 - 06/09/02 08:09 PM Re: What changed, the wire or the breaker?
hurk27 Offline
Member

Registered: 05/15/02
Posts: 71
Loc: Portage, Indiana
It is still classified as a current carrying conductor. didn't think you would have a neutral in an open delta. but you would in a "Y" or center tap (A-C Phase) high leg delta.
_________________________
Be Fair, Be Safe
Just don't be Fairly Safe

Top
#10343 - 06/09/02 08:55 PM Re: What changed, the wire or the breaker?
caselec Offline
Member

Registered: 04/14/02
Posts: 557
Loc: San Jose, CA
Yes, it is current carrying conductor but it only carries the unbalanced load on the single phase winding of the transformer. There is no way all 4 conductors can be full loaded at the same time. 310-15(b)(4). If the conductor ampacity needs to be adjusted because of ambient temperatures then the neutral size would also need to be adjusted.