ECN Electrical Forum - Discussion Forums for Electricians, Inspectors and Related Professionals

ECN Shout Chat
Top Posters(30 Days)
Admin 19
Recent Posts
Anyone hiring inspectors?
by HotLine1. 03/27/17 08:03 AM
Old decora style outlets
by Admin. 03/25/17 11:40 AM
ESA Arc flash course
by TheShockDoctors. 03/24/17 10:15 AM
fuse rejectors
by HotLine1. 03/24/17 07:53 AM
Another Forum Update
by Admin. 03/22/17 03:04 PM
New in the Gallery:
SE cable question
Popular Topics(Views)
231,576 Are you busy
166,374 Re: Forum
160,686 Need opinion
Who's Online Now
2 registered members (geoff in UK, HotLine1), 72 guests, and 13 spiders.
Key: Admin, Global Mod, Mod
Previous Thread
Next Thread
Print Thread
Rate This Thread
#10327 - 06/06/02 09:02 AM Surge Arresters. NEC 280  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Beyond voltage, frequency etc. how are surge arresters sized? The surge arrester will be connected to the service conductors. For this example, would the same size surge arrester be used for a 120/240V, single phase, 100 amp service or for a 120/240V, single phase, 400 amp service?

Frank


Work Gear for Electricians and the Trades

#10328 - 06/06/02 08:39 PM Re: Surge Arresters. NEC 280  
sparky  Offline
Member
Joined: Oct 2000
Posts: 5,303
Frank,
just speculation here, but i would venture that arrestors be sized in accordance to problems external...
It should be given some thought, for the sake of $400 +- of AFCI's in a panel here.


#10329 - 06/06/02 09:23 PM Re: Surge Arresters. NEC 280  
Ron  Offline
Member
Joined: Mar 2002
Posts: 582
White Plains, NY
Many Things to keep in mind.
Voltage ratings
Type of protection (Catagory A = low, B = Medium, C = high exposure to intense surges)
Breif explanation: http://www.currenttechnology.com/paper_2.htm
Good examples and info: http://www.currenttechnology.com/tutorial1.htm

Generally the device does not have an ampere rating because they are conencted in parallel to the protected conductors/equipment.

[This message has been edited by Ron (edited 06-06-2002).]


Ron

#10330 - 06/06/02 11:42 PM Re: Surge Arresters. NEC 280  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
One aspect that seems to get glossed over is the critical minimization of inductive reactance in conductors between the ‘magic black box’ and bus taps. A three-foot run of #4s severely limits the arrestor’s capability to clamp voltage AT THE 400A BUS. Basic laws of physics are often ignored.


#10331 - 06/07/02 08:08 AM Re: Surge Arresters. NEC 280  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Thank you for replies. I'm not up on surge arrester technology. I'll need to study more. Good links. Over the last week or so we've had quite a few storms in Western Pennsysvania.

I had a discussion with my Supervisor concerning the possibility of installing surge arrerstors on line side of service disconnect and T.V.S.S. (Transient Voltage Surge Suppressors) on the load side of the service disconnect in several of our buildings.


#10332 - 06/07/02 12:47 PM Re: Surge Arresters. NEC 280  
Bjarney  Offline
Moderator
Joined: Apr 2002
Posts: 2,527
West-Southern Inner-Northeast ...
There are arrestor packages "listed for use as service equipment," but I'd be sure that the utility will buy into your plan before you show up at a customer’s site with heavy cardboard box in hand. Taps should ideally be installed downstream of the metering but before the servce disconnect. [That may involve breaking a seal, so keep the utility in the loop. It’s a bit embarrassing to have a customer without a day’s worth of power while a dispute is going on.]

It’s crucial to keep the tap conductors as short as possible. The arrestor guys may promise the world, but understand that those numbers can be made instantly worthless because they are based on tests at the arrestor terminals, and surge ratings will always be lower/slower at the other end of the tap.

This text and links are intended ONLY as an example. GE just seems to explain the problem fairly well. They differentiate the connection as “Tee-” versus “Series-connected.” http://www.geindustrial.com/products/applications/choose.pdf http://www.geindustrial.com/products/brochures/9l10f.pdf
GE hawks a true Kelvin-connected series, but they’re limited to a 100-ampere-continuous circuit rating. http://www.geindustrial.com/products/brochures/9l10m.pdf

The only time these comments would not apply is where a equipment company insisted on some blind installation of a ‘showpiece’ arrester to fulfill some mealymouthed insurance or warrantee clause, with no real concern that it had to work properly. That’s where the little blobs with a locknut and three-foot leads prove useful. (Too many arrestor salesguys proudly list Durro-Test in their resumes.)

Regional variations and local customs will determine how this applies to you.


#10333 - 06/07/02 02:41 PM Re: Surge Arresters. NEC 280  
Frank Cinker  Offline
Member
Joined: Jul 2001
Posts: 311
Pennsylvania
Good advice which I will keep in mind.



Member Spotlight
togol
togol
NW In. USA
Posts: 421
Joined: September 2005
Show All Member Profiles 
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box
Powered by UBB.threads™ PHP Forum Software 7.6.0
Page Time: 0.018s Queries: 14 (0.003s) Memory: 0.7846 MB (Peak: 0.9377 MB) Zlib enabled. Server Time: 2017-03-27 18:26:21 UTC