#103087 - 03/20/02 02:25 PM Overcrowded Box!
Joe Tedesco Offline
Member
Registered: 10/07/00
Posts: 2749
Loc: Boston, Massachusetts USA


This mess was discovered in an
entertainment sound and lighting shop located in North Carolina.
_________________________
Joe Tedesco, NEC Consultant
Top
2017 / 2014 NEC & Related Books and Study Guides
#103088 - 03/20/02 04:43 PM Re: Overcrowded Box!
CTwireman Offline
Member
Registered: 02/07/02
Posts: 840
Loc: Connecticut, USA
Well, at least they wrote a disclaimer about the black, red and blue wires being 277.

They forgot to write: "This box is messy and over crowded and contains code violations"

Is 120 and 277 mixed in this box?
_________________________
Peter
Top
#103089 - 03/20/02 07:59 PM Re: Overcrowded Box!
Redsy Offline
Member
Registered: 03/28/01
Posts: 2056
Loc: Bucks County PA
Where's the problem? A simple calculation reveals---
1) There are (3) 1/2" KOs. on each side of the box
2) There are 4 sides
3) That makes (12) 1/2" KOs
4) 1/2" thinwall is good for (9) #12 THWN
5) 9 x 12 = 108 #12s allowed in that box
6) I think there's room for 80 more.
Top
#103090 - 03/21/02 03:37 AM Re: Overcrowded Box!
Electricmanscott Offline
Member
Registered: 01/12/02
Posts: 1457
Loc: Holden, MA USA
They should have used smaller wirenuts!
Top
#103091 - 03/21/02 05:50 AM Re: Overcrowded Box!
olddoubles Offline
Junior Member
Registered: 03/19/02
Posts: 2
Loc: Westwood, NJ, USA
PLEASE! CAN'T I PUT JUST 2 MORE WIRES IN THERE!
Top
#103092 - 03/23/02 09:45 PM Re: Overcrowded Box!
NonLinearLoad Offline
Member
Registered: 03/23/02
Posts: 53
Loc: McHenry, IL. USA
Hmmm, is it ok to put his 277v lighting in with what I'm assuming may be 120v circuits? At least they are warning the next guy. And hopefully he used 12 solid to cut them short, just so they would fit a little better.
12 stranded seems much easier to get into boxes in general, yet to be a packer of sorts, and forget the extension ring at the shop doesn't help either.
Jay
Top
#103093 - 03/27/02 06:38 PM Re: Overcrowded Box!
klein man Offline
New Member
Registered: 03/27/02
Posts: 7
Loc: York, Nebraska
hmmm. Well, lets just hope there's atleast power going through that. I would rip all that out and make it more organized. I cant stand disorganization!!!
_________________________
Crozz
Top
#103094 - 10/30/03 06:03 PM Re: Overcrowded Box!
Knightelectrical Offline
Junior Member
Registered: 10/29/03
Posts: 3
Loc: Germanton,NC USA
Non Linear Load.
200.6 D states:
"Where conductors of different systems are installed in the same raceway, cable, box, auxiliary gutter, or other type of enclosure, one system grounded conductor, if required, shall have an outer covering conforming to 200.6(A) or 200.6(B). Each other system grounded conductor shall have an outer covering of white with a readily distinguishable, different colored stripe other than green running along the insulation, or shall have other and different means of identification as allowed by 200.6(A) or (B) that will distinguish each system grounded conductor." NEC 2002
I wonder which was the neutral, Black, red or blue?
Top
#103095 - 10/30/03 06:42 PM Re: Overcrowded Box!
txsparky Offline
Member
Registered: 05/25/01
Posts: 552
Loc: Magnolia,.Texas U.S.A.
LOL at Redsy!!
It seems way too many so called electricians calculate box fill by that very method.
Yup, I'm tellin you boys they woodint uv give us all them thar knockouts ifn they didnt wan us a usin em!!
_________________________
Donnie
Top
#103096 - 10/30/03 08:23 PM Re: Overcrowded Box!
u2slow Offline
Member
Registered: 09/18/03
Posts: 200
Loc: Salt Spring, BC, Canada
Messy or not... wouldn't a simple extension ring address the box fill issue?
Top
Page 1 of 4 1 2 3 4 >

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 53 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 49
HotLine1 43
gfretwell 18
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals