#10300 - 06/04/02 10:06 PM fluorescent light Q
sparky66wv Offline
Member
Registered: 11/17/00
Posts: 2232
Loc: West Virginia
My partner Joe was troubleshooting "cycling" fluorescent lights in a restaurant yesterday and replaced the electronic ballasts. The lights were 8' pairs in WP fixtures, no vents for heat to escape. They were mounted above the cooking areas in the kitchen and the old ballasts were hot enough to burn your hand.

Today they call back, same symptoms.

I say heat. Fixtures that breathe better or have higher temp ballasts may be a solution.

Agree? Disagree? Any ideas?

Thanks in advance...

-Virgil
_________________________
-Virgil
Residential/Commercial Inspector
5 Star Inspections
Member IAEI
Top
Work Gear for Electricians and the Trades
#10301 - 06/05/02 02:51 AM Re: fluorescent light Q
sparky Offline
Member
Registered: 10/18/00
Posts: 5303
prove your theory, see if they cycle when the kitchen is not in use.....
Top
#10302 - 06/05/02 03:01 PM Re: fluorescent light Q
Steve Miller Offline
Member
Registered: 08/30/01
Posts: 325
Loc: Loudoun Cty, VA
We had that problem in our school kitchens. The electronic ballasts lasted a few months (motorolas were the absolute worst). The old fashioned ballasts lasted longer but not long enough so we finally changed all of the fixtures (in the "no air flow" areas) to the old incandescent stoncos with the glass and cage over the bulbs. 150w bulbs fit and they work fine. Not as efficient but when you consider the cost of constant service calls we think we're ahead.
Top
#10303 - 06/05/02 03:46 PM Re: fluorescent light Q
HotLine1 Offline


Member
Registered: 04/03/02
Posts: 6776
Loc: Brick, NJ USA
Hi:
Sounds like an "inproper use of equipment"..
Check to see if the weatherproof fixture is listed for use inside, in a high ambient temperature location.
It probably isn't listed by the mfg for use in a kitchen with high ambient temperatures.

Heat is the main killer of ballasts. The "old" ones were/are a lot larger in size, and can handle heat for longer periods, but they also are not listed for high ambient temperatures.

John
_________________________
John
Top

Member Spotlight
Member Since: 11/17/00
Posts: 2232
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 52 Guests and 8 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals