Is it mandatory to have 1 metre clearance from the front of a JB that is mounted on the ceiling in an electrical room? The JB has 3/0 in and out that are spliced. Is it O.K. to have less than one metre if it is located above the switchgear?
Top
Tools for Electricians:
#102862 - 02/12/07 06:41 PM Re: JB in Electrical Vault
RobbieD Offline
Member
Registered: 02/23/03
Posts: 231
Loc: Canada
Accessibility of Junction Boxes

CEC 12-3014 (2)

A vertical space of 900mm or more shall be required to provide ready access.