The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Sprinklered equipment 26-008
by bigpapa
Yesterday at 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
Wow, that was close!
by jraef
11/28/16 07:06 PM
Earthquake in New Zeeland
by RODALCO
11/27/16 11:25 PM
Calling all Non-US members!! (Non-US only)
by Tjia1981
11/27/16 06:33 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 15
HotLine1 10
Trumpy 8
Texas_Ranger 8
sparkyinak 7
Who's Online
0 registered (), 106 Guests and 5 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102810 - 12/10/06 08:37 PM garage door circuits
u2slow Offline
Member

Registered: 09/18/03
Posts: 198
Loc: Salt Spring, BC, Canada
Large residential garage. 5 garage door openers. All a 1/2hp 120V motors. Three motors have an 8A FLA, and two have a 6A FLA.

It pains me to have to have 5 individual circuits, but I can't seem to find any way around it. 28-206(a) pretty much kills it... the rest of the rule doesn't seem to apply.

Any ideas?

Top
2014 / 2011 NEC & Related Books and Study Guides
#102811 - 12/16/06 10:33 PM Re: garage door circuits
smokumchevy Offline
Member

Registered: 02/14/03
Posts: 62
Loc: Ottawa, Ontario, Canada
Well, as I see it, reading it to the letter you'd have to run 1- 15A circuit to cover your 2-6A openers, and then one each for you other 8A openers, totaling 4-15A circuits.

Now personally, considering this is a 'residential' or 'personal non-commercial' home garage, and seeing that the chances of more than one opener wld be in use at the same time, I'd have no problem myself running only 1 circuit for all. OR 2 circuits and config them as one for the 6A 6A 8A, and one for the other 8A 8A. OR better yet, 1-15A for a 6A & 8A opener, 1-15A for another 6A & 8A opener, and 1-15A for your last 8A opener, totaling 3-15A circuits.

But in the end your really only saving one or two extra runs to conform properly and only you know your or your customers intent of use, so follow your gut feeling and do as you feel comfortable doing.

-Greg

Top