#102802 - 11/27/06 03:59 PM ungrounded delta and ground fault indication
frank Offline
Member
Registered: 05/29/01
Posts: 374
Loc: windsor ontario canada
CEC rule 10-106 (2) where it states wiring systems supplied by an ungrounded system shall be equiped with a suitable ground detection device to indicate the presence of a ground fault.
How is this accomplished and what constitues a suitable device
thanks
Top
Tools for Electricians:
#102803 - 11/27/06 04:37 PM Re: ungrounded delta and ground fault indication
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
The device is a "ground fault indicator panel". I got one from Eecol a while ago. Willet, in Estevan, Saskatchewan, makes them.

It is three transformer type panel lights. Each is connected betweeen a phase and ground. The indication is that, in the event of a ground fault, one light goes out and the other two get bright.

You can't make your own, though. It wouldn't be CSA approved.
Top
#102804 - 11/27/06 05:19 PM Re: ungrounded delta and ground fault indication
frank Offline
Member
Registered: 05/29/01
Posts: 374
Loc: windsor ontario canada
Im looking at an FPE GIL-600 I guess i'm asking where it would connect to the system.
thanks http://www.schneider-electric.ca/www/en/products/ground/html/gil.htm


[This message has been edited by frank (edited 11-27-2006).]
Top
#102805 - 11/27/06 06:08 PM Re: ungrounded delta and ground fault indication
Sandro Offline
Member
Registered: 12/30/01
Posts: 444
Loc: Stoney Creek, ON, Canada
Simply take it off the splitter, as you would any other load. Make sure it has a fused disconnect too.
Top
#102806 - 11/29/06 04:23 PM Re: ungrounded delta and ground fault indication
bigrockk Offline
Member
Registered: 01/25/03
Posts: 174
Loc: Middle of Canada
One of the systems feeding the plant where I work is a three phase ungrounded 240V Delta system. The ground fault indicators are feed directly from the load side of the main circuit breaker. (This is an old plant circa 1930's )

The ground indicators are just three bulbs connected in a wye arrangement with the centre point connected to ground. Under normal conditions all three lamps glow dimly and at equal intensity. If one phase becomes grounded the two lamps on the ungrounded phases glow brightly (they now see a full 240V) and the lamp on the grounded phase goes out. Pretty simple but it works well.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 101 Guests and 13 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Stack, Scotto, Freecrowder, clee512, Jdscott2005

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals