#102696 - 08/24/06 08:36 AM Conduit in fountains
GETELECTRIC Offline
Member
Registered: 10/22/03
Posts: 172
Loc: toronto canada
Has any body installed conduits in commercial
fountains and if they have what conduit and
connectors do you use.

Thx
Top
Tools for Electricians:
#102697 - 08/24/06 06:09 PM Re: Conduit in fountains
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
Are you talking about an existing fountain or new construction? If existing, try to keep the conduit out of the water, usually the fountain water is treated with chemicals to inhibit growth etc. No telling what this may do to your raceway. If new construction, no reason you couldnt run PVC in the slab, I dont think a fountain would be under section 68, even if it is accessible to the public. Best to check with your AHJ to be sure.
Top
#102698 - 08/25/06 05:06 AM Re: Conduit in fountains
GETELECTRIC Offline
Member
Registered: 10/22/03
Posts: 172
Loc: toronto canada
The conduit is new and has to be in the water
.The manufacturer tells me that I have to use brass pipe(plumbers pipe)which is very expensive.
Top
#102699 - 08/29/06 09:59 AM Re: Conduit in fountains
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
You must treat any fountain where it is even remotely possible for a person to get in as a section 68 installation. I don't know of any Brass raceways for a part 1 installation approved for electrical so you will probably require some documentation on the raceway or get a site approval from CSA, ULC, Warnock Hearsey, etc.
Top
#102700 - 09/19/06 07:10 PM Re: Conduit in fountains
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
section 68 is pretty clear on what it covers. This may fall under "decorative pool" but the dimensions have to larger than 1.5m in any direction. 68-100 does refer to copper rigid conduit and PVC. I have never seen rigid copper, as for PVC you may have to check with Scepter or one of the other manufacturers for approval documentation.
Top

Member Spotlight
Member Since: 02/23/13
Posts: 204
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
1 registered (HotLine1), 111 Guests and 7 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 51
HotLine1 43
gfretwell 17
Trumpy 16
Ruben Rocha 13
 
Newest Members
clee512, Jdscott2005, FAIZAN, Regitest2, sureshazhagai

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals