The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Safety at heights?
by Trumpy
Today at 05:25 AM
Old Bath Fan
by gfretwell
Today at 01:38 AM
Search Function
by Webmaster
Yesterday at 11:13 PM
Forum Software Upgrade coming soon...
by Webmaster
Yesterday at 09:17 PM
ESA Arc flash course
by frank
Yesterday at 04:25 PM
New in the Gallery:
Desk-mounted "power-board"
Top Posters (30 Days)
Webmaster 30
HotLine1 21
Ruben Rocha 16
Trumpy 13
gfretwell 13
Who's Online
0 registered (), 0 Guests and 185 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102602 - 06/20/06 08:18 PM Feeders to Suites and Panel Size!
Cinner Offline
Member

Registered: 12/01/04
Posts: 77
Loc: Kelowna, B.C., Canada
I am currently working in a residential building that has a suite with a 200 amp panel breaker fed from a #2/0, 125 amp Meter. Does this seem reasonable?

Top
2017 / 2014 NEC & Related Books and Study Guides
#102603 - 06/21/06 08:54 AM Re: Feeders to Suites and Panel Size!
mikesh Offline
Member

Registered: 06/07/06
Posts: 614
Loc: Victoria, BC, Canada
Does not Compute to me. The 2/0 copper is ok for 200 amps in a residential panel but the meter is wrong. Is it a 200 amp meter base? and the utility installed a 125 amp meter? If it is a utility meter I might make a call to them and ask if they are installing downsized meters in residential services. Utilities use their own ampacity and demand figures to size their equipment. If it is the utility that decided to put in a 125 amp meter it might be based on their assesment that 200 amps cannot be drawn from that panel because their is just not the load.
A code compliant 200 amp panel must have a 200 amp meter and a 200 amp meter base as well or the main in the 200 amp panel should be 125 amps. Is this the only 200 amp suite panel? It could be fed from a meter stack that did not have a 200 amp socket installed?
I have offered a few thoughts but at the same time I am asking a lot of questions because I need a bit more info to give a definitive answer.

Top
#102604 - 06/21/06 06:41 PM Re: Feeders to Suites and Panel Size!
Cosimo Offline
Junior Member

Registered: 06/21/06
Posts: 6
What size overcurrent protection?
Are you sure it's 2/0 and not #2?

Top