I plan to replace power factor correction capacitors inside a wye-delta starter. Existing capacitors were damaged due to a wiring fault. 26-218 2(d) does not let me put capacitors on the load side of the starter if it is wye-delta starting, but I am replacing existing capacitors, installed by the manufacturer. What gives? Why cant I do this in the field, when it is an accepted industry practice? Any ideas out there? Thanks.
Top
Tools for Electricians:
#102597 - 06/15/06 08:29 PM Re: 26-218
twh Offline
Member
Registered: 03/11/04
Posts: 901
Loc: Regina, Sask.
If I were replacing parts on CSA approved equipment, I would do it in a manner that would restore the equipment to the condition at which it was approved. I don't think that it is up to us to question the CSA approval.

As to it being an industry practice - perhaps it isn't a good practice.
Top
#102598 - 06/16/06 04:12 PM Re: 26-218
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
Ok it has been 15 years since I last wired a Y / delta starter but from memory the y has windings that are shorted in y then open and reconnect delta. So there is a moment where there is no voltage on the wires that were shorted at the y point. Put a capacitor across the output and it would discharge during the transition possibly creating a problem. If I recall, the capacitors should not be connected until the motor reaches operating speed. There may also be tourque issues but on that point I think I am confusing the capacitor in single phase motors with power factor correction capacitors.
I might ask if a factory supplied y/delta with PF correction does not have a set of contacts that don't close until after the motor is Delta?
Top
#102599 - 06/17/06 09:04 PM Re: 26-218
jay8 Offline
Member
Registered: 07/28/05
Posts: 183
Loc: Vancouver, BC
The starter is wired in such a way that the capacitors come online when motor has completed its transition from wye to delta. 26-218 refers to overvoltages and overtorques, reclosings, jogging etc. But because the caps come online after transition, and there is no way these machines I am working with are going to be jogging frequently, I dont see the problem.
Top
#102600 - 06/19/06 04:10 PM Re: 26-218
mikesh Offline
Member
Registered: 06/07/06
Posts: 613
Loc: Victoria, BC, Canada
So Jay I gather your starter is an approved unit that does not connect the capacitors until the motor is to operating mode. So I see no violation here. Approved starter with PF correction included is not the same as making one yourself. Make one yourself and you would be in violation.
Top

Member Spotlight
Member Since: 12/24/00
Posts: 4259
New in the Gallery:
SE cable question
Featured:

2017 NEC and Related
2017 NEC
Now Available!

Shout Box


Who's Online
0 registered (), 94 Guests and 10 Spiders online.
Key: Admin, Global Mod, Mod
 
New in the Gallery:
SE cable question
 
Top Posters (30 Days)
Admin 47
HotLine1 43
gfretwell 19
Ruben Rocha 12
Trumpy 9
 
Newest Members
Freecrowder, clee512, Jdscott2005, FAIZAN, Regitest2

ECN Electrical Forums - sponsored by Electrical Contractor Network - Electrical and Code Related Discussion for Electrical Contractors, Electricians, Inspectors, Instructors, Engineers and other related Professionals