The Electrical Contractor Network

ECN Electrical Forum
Discussion Forums for Electricians, Inspectors and Related Professionals

Books, Tools and Test Equipment for Electrical and Construction Trades

Register Now!

Register Now!

We want your input!

Featured:
   

2017 NEC and Related
2017 NEC
Now Available!

   
Recent Posts
Industrail Control Panel bonding per 409.108
by sparkyinak
22 minutes 4 seconds ago
Calling all Non-US members!! (Non-US only)
by aussie240
12/07/16 02:39 AM
Photo Upload Tutorial
by DanK
12/06/16 11:35 PM
Sprinklered equipment 26-008
by bigpapa
12/02/16 04:24 PM
On Delay Relay with Auto Reset
by Potseal
12/01/16 09:59 AM
New in the Gallery:
12.5A through 0.75mm˛ flex (just out of curiosity)
Shout Box

Top Posters (30 Days)
gfretwell 13
HotLine1 10
sparkyinak 9
Texas_Ranger 8
Potseal 6
Who's Online
2 registered (LongRunner, sparkyinak), 94 Guests and 4 Spiders online.
Key: Admin, Global Mod, Mod
Topic Options
Rate This Topic
#102579 - 06/09/06 09:24 PM red. neutral cec/2006
trevman Offline
Member

Registered: 08/17/05
Posts: 47
Loc: canada
what is the reduced neutral size for a 200 amp residential service in the new code book?
is it table #17 #6 awg.

Top
2014 / 2011 NEC & Related Books and Study Guides
#102580 - 06/12/06 07:04 AM Re: red. neutral cec/2006
Rick Kelly Offline
Member

Registered: 01/11/06
Posts: 60
Loc: Iqaluit, NU, Canada
Your question is rather vague at best.

Table 17 refers to the "Minimum Size of Grounding Conductor". And yes, a #6 is the correct size for a grounding conductor with 200 amp service conductors.

It, Table 17, does not directly have anything to do with the size of the service neutral conductor.

Minimum requirements for the system neutral conductor are detailed in 4-022. In no case may it be smaller then a #10 copper or a #8 aluminum or smaller then the system ground conductor as determined by Table 17.

As well the service neutral conductor must be sized so it can handle the unbalanced load from the system. The size of the "unbalanced load" is based on the demand calculations of section 8.

If you are going to down size a service neutral you had better have the calculations ready to present to the inspector. I'll bet you will be asked for them, I would ask for them.

You might also want to ensure that the CEC 20th edition has been adopted by the AHJ in your region.

Rick Kelly...